So now you need to ascertain whether the problem is faulty appliances or an accumulation of earth leakage
I think it’s accumulation of earth leakage but I will get them to try to eliminate the appliances, What are my options if it is earth leakage?
 
If it is earth leakage then do away with the upfront RCD and change MCBs to RCBOS
Or if you get a clamp you could possibly juggle things round in the board
 
It would be unusual for a domestic to have inrush currents that would justify type C RCD. Also you might find it harder to meet disconnection times with a type C. If everything is unplugged does it trip? I am not sure whether you mean you re-wired the whole house or part of it? If it is a new rewire then the IR readings you are getting are unusually low for new cables installed properly.
 
Hi - if the IR tests are “in the meg Ohms” then it’s likely to be attached equipment. Perhaps turn everything on (plus boiler) and ramp test the tripping RCD. If it now trips below 15mA, start unplugging.
 
Hi - I second ramp test....however....one recent upgrade had the same issue, all tests ok. had customer to unplug anything not in use, tested all appliances...narrowed it down to possibly a cooker fault (still too random to actually id the fault ) new cooker, no issues. Sometimes it is not always black and white. Why not try another rcbo and move a circuit off the main RCD.
 
Several things spring to mind:

That IR reading is far too low for new wire
Did you wire it or just test it
Do you know which circuit has the low reading
Why a big dual board in a new home
Have you ramp tested the rcds
Could you reconfigure the board for rcbo's
Do you have outside circuits

Etc etc
 
Several things spring to mind:

That IR reading is far too low for new wire
Did you wire it or just test it
Do you know which circuit has the low reading
Why a big dual board in a new home
Have you ramp tested the rcds
Could you reconfigure the board for rcbo's
Do you have outside circuits

Etc etc
think OP's remit was a CU change.
 
I read post #3 where he mentioned "existing circuit"
 