Hi - if the IR tests are “in the meg Ohms” then it’s likely to be attached equipment. Perhaps turn everything on (plus boiler) and ramp test the tripping RCD. If it now trips below 15mA, start unplugging.
 
Hi - I second ramp test....however....one recent upgrade had the same issue, all tests ok. had customer to unplug anything not in use, tested all appliances...narrowed it down to possibly a cooker fault (still too random to actually id the fault ) new cooker, no issues. Sometimes it is not always black and white. Why not try another rcbo and move a circuit off the main RCD.
 
Several things spring to mind:

That IR reading is far too low for new wire
Did you wire it or just test it
Do you know which circuit has the low reading
Why a big dual board in a new home
Have you ramp tested the rcds
Could you reconfigure the board for rcbo's
Do you have outside circuits

Etc etc
 
Several things spring to mind:

That IR reading is far too low for new wire
Did you wire it or just test it
Do you know which circuit has the low reading
Why a big dual board in a new home
Have you ramp tested the rcds
Could you reconfigure the board for rcbo's
Do you have outside circuits

Etc etc
think OP's remit was a CU change.
 
I read post #3 where he mentioned "existing circuit"
 
If you talked through with the customer about their choices re RCBO and RCD CU's and explained how situations like this can occur (nuisance tripping/earth leakage) I dont think you owe them anything unless they want you to investigate at their cost.

If on the other hand you didn't talk through options then they are going to blame your work so you'll need to find the faulty appliance/fault at your cost.

Previous advice is as ever, great.

Good luck.
 

Reply to Nuisance tripping. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
356
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
293

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock