P
Pip
Advise Please.
Called out to my local farm, who deal in fruit and veg, to a DOL starter switch which cuts out after a minute or so. This switch controls a 415V 5 amp 3 phase motor running a conveyor belt, and has done so for a number of years.
I replaced the switch with a second hand one I had just see if that was the issue, but to no avail.
Due to low IR readings I rewired from the switch to the motor via the original Cee Form plug and socket, and the on/off switch on the conveyor belt unit, re installed the original switch, but still have the same problem.
So before I advise replacement of the motor, what else could be causing this DOL switch to trip out?
I have not changed any settings on the overload part of the switch.
When it trips out, after a few minutes the switch will work and the motor will start again, (the Bimetal strip cooling down and resetting?)
So would this be the motor drawing more current than stated so overload occurs? or just old switch / overload?
Thanks in advance
Advise Please.
Thanks in advance
Is the DOL starter compatible with the motor, does the Motor need a better way of starting eg Star Delta, is the conveyor blocked in any way causing the Rotor to lock?
check for volt drop across each phase of the contactor
check you have equal current on each of the phase lines
check voltages, have you dropped a phase?
Have you IR tested the windings?
or the sparky's nose test?
power off, open terminal box on top of motor, stick nose close to motor and inhale.
95% effective and saves getting the expensive meter out of the van!!
What you might find is the bearings in the motor at starting to seize or the gear box that the motor is driving has become warn out, you could do with a clamp meter on it and if you adjust the overload up you can see the current rise you might find due to its age that another amp makes the motor continue to run pointing towards increased labouring on the motor. "seen this before"
And compare it with the motor FLA on the nameplate and the current setting of the starter. Surely if the starter keeps tripping on overload, the first thing you would do is see if it is overloaded?
Hi,
As I say it has been working this way for a number of years without a problem, the starter and motor have been a pair for the same period.
The conveyor is not blocked, how freely it travels I can't tell as I have no knowledge of it before the issue, also not sure of the maintenance regime regarding greasing etc but will advise it.
[automerge]1579115204[/automerge]
Hi,
Have not lost a phase, Only briefly checked voltage on each phase before it tripped out but nothing untoward from first impressions, will check current and voltage again. Thanks
[automerge]1579115500[/automerge]
Hi Pete,
No not gone that far, IR tested the feed cables, and changed as I mentioned due to low readings, (and all the cuts and nicks and routing) which is why I'm suspicious of the motor.
[automerge]1579115610[/automerge]
Ha Ha. Have done that, but no strange smells or burning, but might try and get closer and give it another go
[automerge]1579115909[/automerge]
I like the way you're thinking, the motor, and gear casing attached, do move when the shaft of the belt rotates, which does suggest something is not aligned
Will check current as per other reply
[automerge]1579116705[/automerge]
As I say this Switch and Motor have been working together for a number of years without a problem. See pic regarding the motor and switch. The current setting on the overload is at 6.5A, and as I say I have not changed this, but following another reply I will check with a clamp meter and change settings.
Saying that when I swapped the switch out for a second hand one I had I did change the load setting on that one and it still tripped out
ok,
assuming the following is true.
motor is not physically overloaded
if the motor draws 5A at max rated current and the overload is set at the same,
if you measure the current on each phase and it is roughly equal on each phase and less than 5
it is a faulty overload relay
if the currents are unequal then
you have a failure in the circuit on one phase, find it by measuring where the volt drop is.
i.e. measure the voltage between the incoming L1 and the outgoing L1 on the contactor, repeat for other two phases
same again for the overload relay.
note that you can get a phantom voltage on a cable coming back from the motor if you are measuring in reference to earth.
example,
if the contactor has failed on L2 only and not passing any current,
you will still measure 230V from the outgoing terminal to earth or N
the voltage is actually a combination of L1 and L3 going through the motor and returning.
for testing, in the past I have linked out the N.C contacts on the overload relay to allow the contactor to stay energised for long enough to test.
be careful as by doing this for a long period of time, (1 minute or more) you could overheat the motor.
there are a few possible outcomes.
1. contactor has failed on one phase
2. overload relay is faulty
3. cable from overload relay to motor is broken (including any junctions)
4. somewhere upstream of the contactor you are loosing voltage ( isolator, cable, plug/socket, circuit breaker)
5. faulty motor
if you believe it is a faulty motor,
test resistance between star point (terminal in motor casing where 3 are joined) and each of the incoming phase connections.
should be roughly equal
if one is significantly different to the other two then send motor to the rewind shop for investigation.
6.5A is too high, the overload should be set at the FLC for the motor, so acvoridng to your pictures the overload should be set at 5.1A.
How many times have you tried to run the motor like this? It sounds like you've tried it, and it tripped, many times. This is not advisable and could be degrading the overloads.
Test the motor, both continuity and IR, I'm surprised this wasn't your first port of call after a visual check.
Start with a visual inspection of conveyor system. Nearly every time I'm called out to "it's an electrical fault because it keeps tripping" !! It will be a mechanical fault. the fact that the overload has been turned up previously points to this even more so.
If your still can't find the fault then DM as I'm often down Chipping/Blockley way.
ok,
example,
5. faulty motor
Thank you James for a clear and precise evaluation of the situation. I will en devour to follow these instructions and report back.
Again thank you very much
Hi James
Voltage on incoming side of contactor No load
L1 230
L2 238
L3 230
Contactor side with load
L1 218
L2 240
L3 230
Overload side with load
L1 218
L2 240
L3 230
Amps at out going after overload
L1 12.5A
L2 7.6A
L3 1.5A
Resistance between star point and incoming phases at motor all at 2.99 ohms
I presume that you are measuring between a live pin and an earth or N when taking the measurements.
when measuring voltage across the contactor, measure like this.
p.s. it works better when the contactor is under load and use a volt meter instead of a pair of biro's
EDIT,
you should see 0v between incoming and outgoing contacts as in picture.
if you find a voltage between in and out contacts then that is where your fault lies.
after all, a contactor is just a set of mechanical switches, the in and out for each phase should be at the same potential.
Hi James
L1 230
L2 238
L3 230
L1 218
L2 240
L3 230
L1 218
L2 240
L3 230
L1 12.5A
L2 7.6A
L3 1.5A
Definitely a fault on L1 I would check what James has listed It may well be an isolator or supply cable upstream feeding the DOL that is failing causing a high resistive joint looking at the current readings