Do a lot of work for a landlord of commercial properties. Done all the electric work at his 6 units over the last 2 years. General maintenance, changing lights, new circuits.
He now wants to split out the DB keeping just the supply to next door (single phase) and the solar pv on the current DB moving all the other circuits onto a new DB so the use in this unit can be metered as can next door. Bill can then be portioned correctly. He's getting landlord smart meters fitted by an outside company.
He will pay whatever the invoice is and trusts me not to take the mick. Either way its made me doubt my calculations I am going to have to do it over a weekend as both units need to be operational. Don't want to undercut myself as another unit is getting same treatment at end of the year. I have done EICRs last year on all units. No surprises expected.
What's the going rate on a commercial dB these days? Have only done a small commercial change of 6 way 3ph prior. Do lots of circuits and other bits on 3ph Normally busy house bashing and occupied with EV Chargers. Fitted a few 3 pH boards in large domestic conversions.
Will be extending cables where necessary and taking a circuit from this board below to feed new dB and moving all but 2 circuits out of this mess.(solar and supply to next door staying)
Day rate or fixed price? I haven't settled on board yet but do like hager and the schneider ones, the switchgear actually fits and aligns correctly.!
What do you get as unforeseen costs you wouldn't on a domestic...

Thoughts?

As you can see current board is a travesty of a mess and needs sorting
 

Attachments

  • IMG_20200609_144921.jpg
    IMG_20200609_144921.jpg
    188.7 KB · Views: 38
Fixed price, parts plus labour.

It's a small board so without further information I'd give it a full day, allow for a short bit of trunking top and bottom, an adaptable box with din connectors for extending circuits.

I'd go with the schneider Acti9 PoN boards, the plug in N and E connections RCBO's make the job much tidier and quicker than messing around with flyleads.

You'd be better splitting the feed to both boards rather than installing a circuit in one to feed the other, otherwise you end up with an MCB feeding other MCB's which will not achieve discrimination and therefore would be non-compliant.
 
Don't forget to fit SPD and contact Willrose Electrical they are likely to buy those protective devices from you especially the rcbos. At present they are selling them second hand for £53 and the triple pole devices nearly £60.
I am in discussion with landlord about spd.
I got a few of the memshield devices in a box in the van will give them a call.
 
Just had a look and currently they are not taking in stock due to Covid but they will at some point take them off your hands.
 
Just had a look and currently they are not taking in stock due to Covid but they will at some point take them off your hands.
Will keep that in mind. some of the old memshield stuff is very hard to source now. hence the price they charge. I had to buy a 32 amp rcbo for a memshield board last year and paid £49+VAT
 