zenonek

Hi

Im newto this forum and hello to everybody.

Im experienced electrician with 15 years of experience in all kind of domestic premised. Some commertial, but not many..
Niceic Domestic installer for 15 years.

I dont do many Eicr's, s so have troubles coding things.

I realky trying to work to high standards, hence problems with judging others installations.

A friend asked me to do periodic af a building, with 25 studio flats, very small and easy, 4-5 mcbs.
Generally done ok, but some items bugger me a tillle as i wouldnt do them that way.

Installation is 10 years old, last Eicr done 5 years ago by same Niceic addroved contractor who build it 10 years ago.

On last Eicr no codes, bo recommendations....

But i found some items that needs attention.

  • Every single consumer unit have big cable entry hole behind, you can see cavity behing, cons units very dusty inside cause of that, im guesing wind blows , needs to be sealed..... do i code something like this?
  • subfeed 10mm 3 core swa coble to every cons unit not terminated right. Basicaly armour cut and wraped with insulation tape... on other side is propertly glanded.... code it??
  • consumer units ate 2 rcd split boards, plastic, positioned right by the entry doors, inside every flat, i would recommend to replace them for metal, but .... do i code it as c3?

-each flat have one EM light, no test switch and circuit connected to same Mcb as genetal lighting, meaning 2 x 1.0mm cables into one mcb... code it?
- staircase emergency lights have no test switches...
-Every kitchenette appliance is integrated and have isolator above worktop except Microwaves, they are also integrated on a plug behind... code?
-kitchenettes are very small, hence all of the sockets and appliances isolators above worktops are either above sinks, or within 300 from induction hobs or sinks... code?

And finally landlors supply...
  • all external lights permanently on, no sensor or switch, just an mcb.. there used to be a switch but blanked off... code?
  • there is 3 phase consumer unit with 40a mcb's to supply each flat, main switch on that board is rated 200a, same as meter, is rated 200a, but main fuses are 100a, but cores from the street looks like 35mm or even bigger. Meter tails installed are 25mm.
I would do the tails to match 200a board capacity, right? ...code???
  • meter tails terminated to 200a main switch, actualy one, l3 looks black/dirty, not sure its burn, or just dirty, same behind the switch, on enclosure, it may be dirty, but couldnt confirm is, as whole building deened to be switched off, for which i had no permit.. would you code it?
  • 3 ph board not closing propertly, i could see that is resting mostly on msbs, as they were not propertly installed.. is that a code??
  • in same board there is a cover that covers l1 l2 l3 terminals after main switch, and is broken, cracked, attachet to main switch with insulation take.... is that a code?

Any help from experienced tester will be appreciated...

Thank you in advance..
 
Won’t matter unless he’s using they logo would it?


i was about to say that.

I dont mind doing Eicr from time to time, but always making client aware that they will get cert without logo.
[automerge]1593811246[/automerge]
Ok.
Go through them and assign a reg number to each item that it doesn’t comply with. Then in your opinion do you find it to be a C1, C2 or C3?
I’ll give you some feedback when I see what your thinking behind them all is ?
Working on it..
 
Surprising that your clients are happy for an NICEIC DI to inform them he is not deemed sufficiently competent by the NIC to carry out an EICR but allow him to continue anyway?
Just saying.
 
Surprising that your clients are happy for an NICEIC DI to inform them he is not deemed sufficiently competent by the NIC to carry out an EICR but allow him to continue anyway?
Just saying.

That would be an incorrect statement, the NICEIC have not made an statement about his competence.
He has not paid the NICEIC the extra money to put their logo on EICR paperwork, this is not making any judgement about their competence.

However the questions in the OP do suggest a lack of knowledge to carry out EICRs, or even electrical work at all.
 
update..
I wouldn't code any of those. C3 maybe for 527.2.

All our readings are within permitted, an as i said, installation looks very good, except come minor issues.

But i would recommend looking at every single item to improve.
For sure investigate dark spots around main switch, as no evidence of any heat damage to the main switch itself or accessories around.
[automerge]1593871177[/automerge]
emergency lighting not compliant with bs5266 due to lack of testing switches. Turning the mcb will turn off all the lights. ..no code
 
Last edited by a moderator:
However the questions in the OP do suggest a lack of knowledge to carry out EICRs, or even electrical work at all.

No eicr experience? I admit, as you said my post sugest that. For me most installations i see everyday in domestic premises qualify for money back
But which part of my post sugest lack of knowledge of electrical work?
 
No eicr experience? I admit, as you said my post sugest that. For me most installations i see everyday in domestic premises qualify for money back
But which part of my post sugest lack of knowledge of electrical work?

Your suggestion that 25mm meter tails for a supply fused at 100A are too small because the main switch is rated at 200A.
Your comment on the emergency lighting being connected to the normal lighting circuit.
 
And also your question of whether you should code an MCB having two 1mm cables in it.
 
That would be an incorrect statement, the NICEIC have not made an statement about his competence.
He has not paid the NICEIC the extra money to put their logo on EICR paperwork, this is not making any judgement about their competence.

However the questions in the OP do suggest a lack of knowledge to carry out EICRs, or even electrical work at all.
In fairness it's not about paying the NIC extra money. The reason is that ACs are assessed on periodic inspections if that is part of the scope of works which they undertake. DIs are solely for notifying domestic work in England & Wales. This is all they're assessed on. They can apply to have periodic inspection and testing added but it requires additional assessment.
 
Your suggestion that 25mm meter tails for a supply fused at 100A are too small because the main switch is rated at 200A.
its what i would do, match tails to the MS, not to the fuse. Fuse can be replaced for a bigger one by anyone, all kind of maintenance people have access.

Your comment on the emergency lighting being connected to the normal lighting circuit.

you got it wrong, it was a comment only, my issue was 2 radials on one mcb, not EL on lighting circuit.

And also your question of whether you should code an MCB having two 1mm cables in it.

I wouldt do it. in fact i failed niceic assesment years ago for same reason. Connected single light to existing circuit.
[automerge]1594037224[/automerge]
In fairness it's not about paying the NIC extra money. The reason is that ACs are assessed on periodic inspections if that is part of the scope of works which they undertake. DIs are solely for notifying domestic work in England & Wales. This is all they're assessed on. They can apply to have periodic inspection and testing added but it requires additional assessment.

And i agree with you 100%

Its the reason i just DONT DO EICR''
Main reasons as someone mentioned already, i would not get the job, without my scheme support (LOGO)
-there are tons of testers that do eicrs for 100-150, with lots of "limitations" within one hour, agency, or landlord, or ins company they just see Satisfactory, nothing else. I wouldnt sleep at night doing that.

If i do one per year, thats it, its because person ordering the test is contractor im working with for years, and he values the way i do electrics, and he is not only after report.

Anyone willing to advise, thank you, but i remember years ago, first time electrical question on similar forum like this one, almost was eaten alive by "old electricians". on the end didnt get my answer, and i thought that what forums are, to help each other! Save it, dont do it please.
 
Last edited by a moderator:
2 cables connected into 1 MCB is still 1 Circuit though, not a cat in hells chance you failed a NIC assessment for that. Every ring main has 2 conductors in 1 MCB
[automerge]1594042621[/automerge]
And getting into a chamber to swap 100A fuses for 200A ain’t something anyone could do.
 
2 cables connected into 1 MCB is still 1 Circuit though, not a cat in hells chance you failed a NIC assessment for that. Every ring main has 2 conductors in 1 MCB
[automerge]1594042621[/automerge]
And getting into a chamber to swap 100A fuses for 200A ain’t something anyone could do.
yea, but ring is one circuit not 2 radials.
and yes, i have failed, and i thought it was not fair then, but now it does make sense to me.
Or maybe life is just unfair for Di's, ... on one assessment i had no grommet on first socket i was asked to open, explained my self to the guy, builders moved socket without my knowledge slightly to the right, client confirmed that on site.. spend 2 hours showing every possible connection then.
Inspector was satisfied, but in his report included missing grommet, and i was turned down by head office, not the inspector, because of silly builder.
 