Sorted.
Ive subcontracted eicrs to another company. £90 per flat. Niceic approoved contractors. Happy!
Ill do the remedial works
Let see what they will say.
 
can somene please comment on this swa please. I wuldnt do it that way,but need t know if you will find it on yur eir, will you pass it? third core is used as cpc, and armour earthed on the other side 20200702_092010.jpg
20200702_092010.jpg
 

Attachments

  • 20200702_091935.jpg
    97.1 KB · Views: 37
its what i would do, match tails to the MS, not to the fuse. Fuse can be replaced for a bigger one by anyone, all kind of maintenance people have access.

you got it wrong, it was a comment only, my issue was 2 radials on one mcb, not EL on lighting circuit.

That's nonsense, you size cables according to the OCPD rating, not the highest rated switch in a circuit!

2 conductors in one MCB is perfectly acceptable, and is still only one circuit.
[automerge]1594059693[/automerge]
More worrying that a DI is doing commercial work ?

I know, it's absolutely shocking isn't it.

I'll have to stop doing all of the commercial and specialist work I do and get back to domestic work since I am after all 'only a DI'
 
I have not even got domestic installer, doesn't mean I could not do the work, just that i can't self certify.
therefore i will stick to the easier stuff that requires no silly registration.
like 3 phase motors and controls!!
 
subfeed 10mm 3 core swa cable to every cons unit not terminated right. Basicaly armour cut and wrapped with insulation tape... on other side is property glanded 522.8.5 c2

How do you know it's not supported correctly? It could be.
As the armour is not being used as the protective conductor as long as one end of the armour is properly glanded and earthed it's ok (but not what I would do either).
 
there any requirement to fill any gap between the cables and the edge of the qu
subfeed 10mm 3 core swa cable to every cons unit not terminated right. Basicaly armour cut and wrapped with insulation tape... on other side is property glanded 522.8.5 c2

How do you know it's not supported correctly? It could be.
As the armour is not being used as the protective conductor as long as one end of the armour is properly glanded and earthed it's ok (but not what I would do either).
Thank you! what will you say about big hole behind CU to cavity wall? Cavity plasterboard on timber.
 
I have not even got domestic installer, doesn't mean I could not do the work, just that i can't self certify.
therefore i will stick to the easier stuff that requires no silly registration.
like 3 phase motors and controls!!
I’ll help ya out mate ??
 
not impossible...especially that 200A MS is clearly visible! its what i learned a while ago, protect yourself from stupidity of other people.
it is no code probably, but as inexperienced in eicr im asking for advise, right?

So your saying that becuase the main switch is 200A someone might replace 100A fuses with 200A fuses?
If they are going to do that then how do you know they would fit 200A fuses and not 300A or 400A? Maybe you should size everything for a nice round 1000A just in case?

My point here is that trying to 'protect yourself against the stupidity of other people' is impossible and quite pointless.

If someone is going to come along in the future and replace a fuse with one of twice its rating then they aren't going to worry about what is written on any switchgear before they do it!

Sometimes I install a 20A DP switch to isolate external lights on a normal 6A lighting circuit, but I sure as he'll don't wire the whole circuit in 2.5 just because there's a switch rated at 20A in the circuit!
 
So your saying that becuase the main switch is 200A someone might replace 100A fuses with 200A fuses?
If they are going to do that then how do you know they would fit 200A fuses and not 300A or 400A? Maybe you should size everything for a nice round 1000A just in case?

My point here is that trying to 'protect yourself against the stupidity of other people' is impossible and quite pointless.

If someone is going to come along in the future and replace a fuse with one of twice its rating then they aren't going to worry about what is written on any switchgear before they do it!

Sometimes I install a 20A DP switch to isolate external lights on a normal 6A lighting circuit, but I sure as he'll don't wire the whole circuit in 2.5 just because there's a switch rated at 20A in the circuit!
im not trying to argue with you, and im not asking it it is ok for me to do it, i just do it, and you dont have to agree with it.
and why would someone install 300a fuse if ON THE BOARD SAYS 200A Max.
But HEJ, even if they do im covered, as my TAILS and MS is 200A rated max! (load also matters)

And there is a difference between 20a and 100a in terms of harm it can cause, bad example.
 
im not trying to argue with you, and im not asking it it is ok for me to do it, i just do it, and you dont have to agree with it.
and why would someone install 300a fuse if ON THE BOARD SAYS 200A Max.
But HEJ, even if they do im covered, as my TAILS and MS is 200A rated max! (load also matters)

And there is a difference between 20a and 100a in terms of harm it can cause, bad example.

The same reason that they would replace a 100A fuse with anything bigger than 100A, a lack of knowledge or common sense.

Yes there is a difference between 20A and 100A, I am well aware of that, but the point is the same, the conductors need only be rated for the OCPD they are protected by not for the rating of whatever switch happens to be installed.

20A can cause a significant amount of harm, in terms of cable sizing, or more specifically incorrect cable sizing, then it can do exactly the same harm as 100A.
 
The same reason that they would replace a 100A fuse with anything bigger than 100A, a lack of knowledge or common sense.

Yes there is a difference between 20A and 100A, I am well aware of that, but the point is the same, the conductors need only be rated for the OCPD they are protected by not for the rating of whatever switch happens to be installed.

20A can cause a significant amount of harm, in terms of cable sizing, or more specifically incorrect cable sizing, then it can do exactly the same harm as 100A.
according to esqcr and osg meter tails domestic should be at minimum 25mm2, why would that be if 60a fuse installed...maybe because fuse can easy be replaced with 100A...
Im not saying that you are wrong, im just saying I would match tails to MS, unless MS rated lower that fuse. i dont think im wrong either.
 
according to esqcr and osg meter tails domestic should be at minimum 25mm2, why would that be if 60a fuse installed...maybe because fuse can easy be replaced with 100A...
Im not saying that you are wrong, im just saying I would match tails to MS, unless MS rated lower that fuse. i dont think im wrong either.
If Main Switch is rated lower than the fuse, then you are quite likely to have problems. Main Switch should be rated equal to or higher than the fuse, and the tails should be sized to suit the fuse.
 
Yes. Didnt want to say that. I dont know why i said that.. makes no sense:tongueout:
[automerge]1594076220[/automerge]
I had diferent scenario in my head 100a fure, 25mm tails and ie 60a isolator with 60a fuse in it..
[automerge]1594076511[/automerge]
It was just an example
 
Last edited:
according to esqcr and osg meter tails domestic should be at minimum 25mm2, why would that be if 60a fuse installed...maybe because fuse can easy be replaced with 100A...
Im not saying that you are wrong, im just saying I would match tails to MS, unless MS rated lower that fuse. i dont think im wrong either.

Can you post a direct quote from the ESQCR to support this?

The OSG is just a guide and is not regulation, BS7671 does not put any minimum size on meter tails.

You are wrong, conductors are not sized according to the rating of a switch they are connected to!
 
This is why:



I'm a DI but I do a lot of commercial and unusual/specialist work so I disagree with the suggestion that a DI shouldn't be doing commercial work.
I know a few electricians that opted for DI that do majority commercial work, only reason to get around the notification scam in the domestic sector.
Its a cheaper option.
 
That would be an incorrect statement, the NICEIC have not made an statement about his competence.
He has not paid the NICEIC the extra money to put their logo on EICR paperwork, this is not making any judgement about their competence.

However the questions in the OP do suggest a lack of knowledge to carry out EICRs, or even electrical work at all.
Fair point, clearly yours and other subsequent posts show many DI's are doing commercial work and are clearly competent to carry out EICR's, but use the DI route only as a cheaper means of enabling their domestic work to be notified.
 
This is why:



I'm a DI but I do a lot of commercial and unusual/specialist work so I disagree with the suggestion that a DI shouldn't be doing commercial work.
ah, Ok. Being in Scotland we dont have DI's but I always thought the NICEIC didnt allow commercial/3 phase work under the DI scheme. Thats where my comment was aimed. Obviously wrong.
 

Reply to EICR some help please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
391
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
804
Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock