Ok.
Go through them and assign a reg number to each item that it doesn’t comply with. Then in your opinion do you find it to be a C1, C2 or C3?
I’ll give you some feedback when I see what your thinking behind them all is ?
Every single consumer unit have big cable entry hole behind, you can see cavity behing, cons units very dusty inside cause of that, im guessing wind blows , needs to be sealed.....
527.1.1 and 527.2.1 c2 or c3
subfeed 10mm 3 core swa cable to every cons unit not terminated right. Basicaly armour cut and wrapped with insulation tape... on other side is property glanded
522.8.5 c2
Consumer units are 2 rcd split boards, plastic, positioned right by the entry doors, inside every flat, i would recommend to replace them for metal, but .... do i code it as c3? -
421.1.201 c3 as located right be the only entrance doors without any enclosure
Every kitchenette appliance is integrated and have isolator above worktop except Microwaves, they are also integrated on a plug behind...
No code, 13a plug behind
kitchenettes are very small, hence all of the sockets and appliances isolators above worktops are either above sinks, or within 300 from induction hobs or sinks.
512.2 no code as no water or heat damage.. just reconfirmed its 100mm from hob
And finally landlors supply... all external lights permanently on, no sensor or switch, just an mcb.. there used to be a switch but blanked off... code?
537.3.1 no functional switching c3, also part l br, as on all the time.
there is 3 phase consumer unit with 40a mcb's to supply each flat, main switch on that board is rated 200a, same as meter, is rated 200a, but main fuses are 100a, but cores from the street looks like 35mm or even bigger. Meter tails installed are 25mm. I would do the tails to match 200a board capacity, right?
no code
meter tails terminated to 200a main switch, actually one, l3 looks black/dirty, not sure its burn, or just dirty, same behind the switch, on enclosure, it may be dirty, but couldn't confirm is, as whole building needed to be switched off, for which i had no permit.. would you code it?
suspected cable incorrect termination. No obvious damage, needs investigation f1
3 ph board not closing properly, i could see that is resting mostly on msbs, as they were not properly installed.. is that a code?? in same board there is a cover that covers l1 l2 l3 terminals after main switch, and is broken, cracked, attached to main switch with insulation take.... is that a code?
134.1.1 c3 as no immediate danger...
[automerge]1594050018[/automerge]
Ok, the 200A Main switch is irrelevant, there are loads, and I mean loads of three phase boards with 125A Main Switches on 100A Incomers What type of fuses are currently in place, is it a standard 3 phase cutout or is it in a fuse chamber?
Just one board, with 40a type b mcbs for each flat.
Original electrical installation certificate is written as one installation.
From 40a mcbs to single phase meters, from meters to flats.