The main reason for the S type RCD in France is to prevent the customer from using more power that the tariff they pay for, cynical me.![]()
How is that possible? I thought RCDs did not respond to over current.
The main reason for the S type RCD in France is to prevent the customer from using more power that the tariff they pay for, cynical me.![]()
So really more of an RCBO?The French Disconjoncteur de branchement do, if you go beyond your payed for tariff they trip out, the new Linkey meters are even more sensitive and have less head room that the previous Disconjoncteur.
How is that possible? I thought RCDs did not respond to over current.
RCD is a term which covers a group of similar devices.
RCCB (residual current circuit breaker) works only on residual current and is what is often referred to as an RCD
RCBO (residual current breaker with overcurrent protection) combines residual current and overcurrent operation, often described as an MCB and RCD combined.
SRCD (socket outlet incorporating residual current device) does what it says on the tin (similar to a USA GFCI outlet but does not provide any protection for outgoing cables which I believe they do in the USA)
There are others, but I can remeber all the acronyms or what the stand for, CBR, RCM spring to mind.
All of them are RCDs,
The French Disconjoncteur de branchement do, if you go beyond your payed for tariff they trip out, the new Linkey meters are even more sensitive and have less head room that the previous Disconjoncteur.
It is probably because until recently most supplies were run overground, particularly in rural areas.Why does France mandate TT earthing?
So really more of an RCBO?
Realistically the SP+SN option for RCBO is more useful in terms of allowing N-E faults to be identified and circuit testing performed without much cable removal. but not very common outside of the Wylex/Crabtree ones in the UK it seems.
la-340266305880&gclid=Cj0KCQjwvIT5BRCqARIsAAwwD-T-OkK3xC9qx6Ofe4mhKBpHmtqGcCJ8PhgpPy-TfXe3xeZGtxGxliMaAlHeEALw_wcB&gclsrc=aw.dsFrance is rather spread out with small villages miles apart, so it's more cost effective to run the power supplies overhead as phase and neutral and legislate that it's the occupiers responsibility to provide the earth, different in large towns, but even they are spread out.
Would you want a neutral to break on 3 phase?I've noticed that. Mainland EU always goes DP and SPSN... but the UK seems to have no concern. Do neutrals not break in the UK?
Would you want a neutral to break on 3 phase?
Sorry disconnected from what?