Even with a nominally safe shower that is correctly earthed to the supply but the bath metalwork is not properly bonded as well you can get ten-ish volts of a difference. When wet that is noticeable!
But far more worrying is under fault conditions (PME open, some scroat stealing the sub-station neutral, etc) that could even become fatal.
[automerge]1601498984[/automerge]
There was a time when supplementary bonding was the norm, in fact it became quite ridiculous at times (joking about standing still long enough and you would get some green/yellow wire attached to an ankle...).
But today there is a view, more of a slightly misplaced trust, that an RCD will save you no matter what. Sure RCD protection should be the norm, but it is not (in my mind) an excuse for not having extraneous parts properly bonded (i.e. metal gas & water pipes, possibly some other things as well), and in some cases supplementary bonding to be sure that no stray potential appears in wet conditions, etc.
But far more worrying is under fault conditions (PME open, some scroat stealing the sub-station neutral, etc) that could even become fatal.
[automerge]1601498984[/automerge]
There was a time when supplementary bonding was the norm, in fact it became quite ridiculous at times (joking about standing still long enough and you would get some green/yellow wire attached to an ankle...).
But today there is a view, more of a slightly misplaced trust, that an RCD will save you no matter what. Sure RCD protection should be the norm, but it is not (in my mind) an excuse for not having extraneous parts properly bonded (i.e. metal gas & water pipes, possibly some other things as well), and in some cases supplementary bonding to be sure that no stray potential appears in wet conditions, etc.