J

johnpaul

I have two 1200w Mini Cookers which trips the current. If I use a 2500w kettle, it is OK. If I use a 2000w fan heater it is OK. I cannot see any faults with the cookers and cannot get my head round what is happening. Any help appreciated?
 
When you say ‘the current’ do you actually mean the rcd ?

could be a leaky element
 
Most likely issue is a fault with each of the cookers.
The rcd is doing its job correctly by turning the power off when it detects a fault.
 
if the mini cookers have been out of use for a while, there could be damp in the elements. one way to dry them out is to plug into a socket that doesn't have RCD protection and run them for a while.
 
An RCD doesn’t give overload protection, so adding up the wattage doesn’t give any clues.

it may be a faulty element, or faulty connection within either appliance.

Do the work ok separately?

Is it one rcd for a number of circuits? (Cumulative?)
 
Fault with the element would be my guess. A PAT test (yes yes I know) would reveal the fault.

RCD trips due to current in L and N not being equal (leaking to earth). Of the appliance however tests fine then you're looking at something else but my money is the appliances, elements specifically.

Thought I posted this last night ?
 
An RCD doesn’t give overload protection, so adding up the wattage doesn’t give any clues.

it may be a faulty element, or faulty connection within either appliance.

Do the work ok separately?

Is it one rcd for a number of circuits? (Cumulative?)
Yes one RCD for all circuits.
 
I bought a new oven and all is OK, but have no idea what is wrong with the old one.
Is there any way to check?
 