How would you code this?
A 8kw shower (so pulling ~37A) is protected by a B32 breaker. 6mm² cable rated at 47A, ref method C
(Actually, that last bit isn't true. In fact it's currently ref 101 = 27A, but an easy fix to get it to ref C, so for the sake of the discussion, let's pretend it's ref C)
I'm torn between C2 and C3. I suspect it's technically a C2, but after at least several years like this (date on shower 2014, circuit installation date 1997), and with no apparent ill effect on any of the equipment, I find it difficult to sell it to the client as potentially dangerous.
A 8kw shower (so pulling ~37A) is protected by a B32 breaker. 6mm² cable rated at 47A, ref method C
(Actually, that last bit isn't true. In fact it's currently ref 101 = 27A, but an easy fix to get it to ref C, so for the sake of the discussion, let's pretend it's ref C)
I'm torn between C2 and C3. I suspect it's technically a C2, but after at least several years like this (date on shower 2014, circuit installation date 1997), and with no apparent ill effect on any of the equipment, I find it difficult to sell it to the client as potentially dangerous.