I think so, especially if its the type that does, nt require installing a rodWould it not be better and easier to install a pen fault device as they do for EV?
like a Garo G6EV40PME Consumer Unit, MCU Type A RCBO & PME Fault, EV Charger Compatible
I think so, especially if its the type that does, nt require installing a rodWould it not be better and easier to install a pen fault device as they do for EV?
like a Garo G6EV40PME Consumer Unit, MCU Type A RCBO & PME Fault, EV Charger Compatible
Except, and CBA looking up the numbers, the regs prohibit switching the earth. Or they did until the latest edition which ...Instead of making a metal outbuilding TT and having a high impedance electrode and then relying on RCDs and having the possibility of 2 earthing systems in close proximity, could you use an earth electrode (for measurement only) and a voltage monitoring relay that opens a contactor (L, N & PE) if ...
allows switching of the earth, and in fact requires it, for EVsIndeed yes I do feel like it is an incomplete solution, but better than nothing especially if the item in question is unlikely to be touched etc (unlike an EV)
Its a very poor situation IMHO when we are now looking at the 18th edition of BS7671 with all the regulations contained there in. And we still have a possible situation where the whole lot can become live to the touch, bypass every protective device in the install, and the only way its addressed is to fit oversized bonding and hope the potential victim is wearing thick soled shoes. Its about time PME issues like this were addressed with safety monitoring devices that cut the supply at the origin should a loss of neutral occur.Except, and CBA looking up the numbers, the regs prohibit switching the earth. Or they did until the latest edition which ...
allows switching of the earth, and in fact requires it, for EVs
As already said, you can extend the PME to the outbuilding if you BOND any extraneous conductive parts adequately. That mean min 10mm2 of copper, or more if calculations say so. If the bonding is inadequate in cross section, then under fault conditions it'll melt.
Yes, teh same argument apply within the main dwelling - which is why we have main, and if required supplementary, bonding to create an equipotential zone.
So is switching of the earth prohibited, but only allowed for EV charging?, and therefore if you used a device (matt-e, garo etc etc) to protect against a PEN fault by switching the earth but not for an EV but instead for an outbuilding or hot tub or similar would that be prohibited as the only mention of switching the earth is in EV charging section?, seem a bit of a gray areaExcept, and CBA looking up the numbers, the regs prohibit switching the earth. Or they did until the latest edition which ...
allows switching of the earth, and in fact requires it, for EVs
As already said, you can extend the PME to the outbuilding if you BOND any extraneous conductive parts adequately. That mean min 10mm2 of copper, or more if calculations say so. If the bonding is inadequate in cross section, then under fault conditions it'll melt.
Yes, teh same argument apply within the main dwelling - which is why we have main, and if required supplementary, bonding to create an equipotential zone.
ArgeeIts about time PME issues like this were addressed with safety monitoring devices that cut the supply at the origin should a loss of neutral occur.
For the vast majority of sheds, if there is an extraneous part it's likely to be the waterpipe. I would be inclined to insert a section of plastic pipe and convert it to "un-extraneous" (is that English?). Less hassle at times, than running out a 10mm earth.As already said, you can extend the PME to the outbuilding if you BOND any extraneous conductive parts adequately.
Car parked next to shed bond it, metal gate bond it, lady walking by with a pram bond it. rubbish me steel toe caps !! bond it ??Metal walls, metal roof , grill floor , all bonded
A figurative red warning flag has been waving over the dangers of the TNC-S supply system for some time now. You do wonder if it will take a high profile incident (hopefully not) to raise awareness to a point where definate steps must follow. That was literally what happened to cause the introduction of rcd,s into mainstream electrical installation work.Its a very poor situation IMHO when we are now looking at the 18th edition of BS7671 with all the regulations contained there in. And we still have a possible situation where the whole lot can become live to the touch, bypass every protective device in the install, and the only way its addressed is to fit oversized bonding and hope the potential victim is wearing thick soled shoes. Its about time PME issues like this were addressed with safety monitoring devices that cut the supply at the origin should a loss of neutral occur.
In the meantime I will stick with my thoughts that extending TNC-S to a wooden outbuilding is fine, TT my preferred option, but I will never use both methods together. Just my preference. Wonder if the 19th edition will come up with something else to fit into your TNC-S compliant, Non combustible, SPD and RCBO filled C/U. its gonna get crowded in there. ?
Manufacturers of EV charging stations are already on the case ?A figurative red warning flag has been waving over the dangers of the TNC-S supply system for some time now. You do wonder if it will take a high profile incident (hopefully not) to raise awareness to a point where definate steps must follow. That was literally what happened to cause the introduction of rcd,s into mainstream electrical installation work.
How can you Code the loss of a PEN connection when no mention of this is made in BS7671. I really don't get people's obsession with PEN losses.The garage supply is nothing more than a glorified extension lead or submain radial supply if you like. Connecting back to the mains position, and its the mains position that's the origin of the supply, and that's where your PME is. Your extending the earthing arrangement yes but not exporting the pme. As far as coding I wouldn't. If that's worthy of a code then our nice new metalclad boards are all C2s if PENs lost.