Good resource Glenn!
I have always extended the equipotential zone from a PME and run a 10mm bonding cable if required so have not looked into the option of a TT for an out building in any great depth.
Your resource has got me thinking about the TT option:
It states :
'Where the installation in the garage is supplied by an armoured cable, the armour or any protective conductor in the cable must not be connected to and must not be simultaneously-accessible with any exposed-conductive-parts in the outbuilding.'
1. I'm assuming the armour of the SWA cable is earthed at the supply end (ie main CU in house), it will then be simultaneously accessible with the earthing bar in the outbuilding CU (if the SWA has been glanded in the outbuilding CU).
2. Similar to the above, if the outbuilding CU is metal then again if the SWA cable is glanded in that CU it will connected to the TT earthing system?
3. The neutral of TNCS or TNS is connected to earth at the transformer or cut out, so is it not a problem that the neutral bar in the outbuilding CU is simultaneously accessible to the earth bar in the outbuilding CU?
Cheers guys