16mm twin and earth main supply to storage heater board, no mechanical protection or earthed outer sheating ? No upfront rcd only a bs1361 50amp fuse.

Here’s the updated version including your

Observation:
The inspected apartment contains two consumer units. We were instructed to carry out an EICR on the storage heater board, which is fed via a separate Economy 7 meter located in a communal cupboard on the ground floor. Our inspection found that all Economy 7 supplies in the building are fed from this meter and individually protected via double pole switch fuses containing 50A BS 1361 fuses.

The outgoing cable from each switch fuse is standard PVC twin and earth, which ascends the wall with no mechanical protection as far as could be determined. Within the apartment (first floor), the storage heater consumer unit is fixed to a plasterboard wall. There is a large, unsealed hole behind the unit where the cable enters, and again, no mechanical protection is provided.

The installation is wired in old (pre-2004) colour codes, with no evidence of prior inspection or testing. Based on condition and materials, the installation appears to be approximately 30 years old.

The client has informed us that the landlord or building owner has been made aware of our findings but has expressed frustration regarding the observations.

Classification:
C3 – Improvement Recommended

Regulation Reference:
BS 7671:2018+A2:2022 Regulation 522.6.202 – Cables concealed in a wall or partition at a depth of less than 50 mm from the surface must be provided with additional protection by an RCD not exceeding 30 mA or enclosed in earthed conduit/trunking or protected against penetration.
 
Sorry the landlord / building operator believes it isn't an issue and has never been flagged previously. In the previous job notes it stated a electrical danger notice was issued for bno equipment also but not highlighted the danger.
 
It’s a C3…. It is not an “issue”

No work is actually needed.


Regulations change, and something that was once ok, is now a C3…. Other C3’s could now be C2. Especially before harmonisation. The use of RCDs has became much more spread for example.
 
Absolutely fine when it was installed, no reported signs of deterioration, but does not comply with the current regs, so C3.
There are a few things which were installed to the regs at the time would now be considered dangerous, but this isn't one of them.
 
Absolutely fine when it was installed, no reported signs of deterioration, but does not comply with the current regs, so C3.
There are a few things which were installed to the regs at the time would now be considered dangerous, but this isn't one of them.
Yeah this is what I have it as
It’s a C3…. It is not an “issue”

No work is actually needed.


Regulations change, and something that was once ok, is now a C3…. Other C3’s could now be C2. Especially before harmonisation. The use of RCDs has became much more spread for example.
Thanks for the clarity. In essence, it's worth noting and just making them aware. I suppose with these EICRs, a lot of installations are still in good working order; it's just our ever-changing landscape of the IET regs that keeps us on our toes!
 
Absolutely fine when it was installed, no reported signs of deterioration, but does not comply with the current regs, so C3.
There are a few things which were installed to the regs at the time would now be considered dangerous, but this isn't one of them.
Again, you've put that across very well, many installations out there still that are in good working order, maybe more than the latter ones, unfortunately.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
16mm twin and earth main supply?
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
Tooly1,
Last reply from
DefyG,
Replies
13
Views
430

Advert

Back
Top