Instead of making a metal outbuilding TT and having a high impedance electrode and then relying on RCDs and having the possibility of 2 earthing systems in close proximity, could you use an earth electrode (for measurement only) and a voltage monitoring relay that opens a contactor (L, N & PE) if the voltage between PME earth and the electrode is >50v , although I guess there is a risk of N current and fault current going down said electrode if things went wrong so would probably need 10mm bonding, doh ?


Can 722.411.41 (iv) be applied to a metal outbuilding using a PME earth also, so using a voltage sensing relay and a contactor to break L, N & PE if the voltage is outside of 207v - 253v, to lower the risks (although doesn't make them go away), I know 722.411.41 is for EV but but could the same idea be used in this case
 
It might not be 230v, could be more or less depending on phase balance, Perhaps we need to contact all our neighbours on our local transformer and get everyone to use there oven, tv and electric shower, etc all at the same time of day so the phases stay balanced, then no voltage on CPC in a PEN fault , hahahaha ?
Correct. There are so many variables involved in determining what voltage will eventually be present under open PEN that I usually just assume worst case scenario (for purposes of discussion)
 
Can 722.411.41 (iv) be applied to a metal outbuilding using a PME earth also, so using a voltage sensing relay and a contactor to break L, N & PE if the voltage is outside of 207v - 253v, to lower the risks (although doesn't make them go away), I know 722.411.41 is for EV but but could the same idea be used in this case
Can't see any reason why not. You still feel though that the sulutions we are currently endeavouring to supply for TNC-S issues are not ideal. Reality is TNC-S as a "supply system" is not ideal.
 
Can't see any reason why not. You still feel though that the sulutions we are currently endeavouring to supply for TNC-S issues are not ideal. Reality is TNC-S as a "supply system" is not ideal.
Indeed yes I do feel like it is an incomplete solution, but better than nothing especially if the item in question is unlikely to be touched etc (unlike an EV)

Shame we dont have access to all 3 phases in houses, its quite easy to detect a PEN fault with 3 phase
 
Just realised this thread was about 5 years old.
Mmm, but quite relevant at the moment, with so many home offices going in
But you haven't read GN8. Surely this would be a good starting point?
Maybe.I probably will get a copy eventually. Unfortunately I can't afford a full set of Guidance
But you haven't read GN8. Surely this would be a good starting point?
Maybe. Unfortunately I cannot afford a full set of Guidance Notes at the shocking price they are available & I am still working through Sparky Ninja's online webinars, which are more accessible & certainly cheaper... Some good stuff on earthing.
I probably will get GN8 eventually, but probably by the time I have finished Sparky Ninja's resources a new edition will be out.
What I am really interested in regarding earthing & I suspect not covered by GN8, is how to go about fitting an earthing mat when I have my drive done that will help me in future to use my Solar power off-grid ("Islanding"). I gather from Sparky that proposed standards talk about earthing mats for new builds, e.g adding them to foundations, but no guidance on retro-fitting.
 
TT and PME joined happily together.
Broken PEN upstream of yer supply with Mrs Jones at number 42 having a shower and Mr Smith cooking the Sunday roast at 48. Every buggers supply load see's yer poor old Rod as a brightly shining light is seen by moths. Best keep em separate, Mind you if its a nice wooden floored shed with no bonding needs even the swa glanded properly will often be a good enough cpc for extending yer TN-C-S arrangement.
 
Mmm, but quite relevant at the moment, with so many home offices going in

Maybe.I probably will get a copy eventually. Unfortunately I can't afford a full set of Guidance

Maybe. Unfortunately I cannot afford a full set of Guidance Notes at the shocking price they are available & I am still working through Sparky Ninja's online webinars, which are more accessible & certainly cheaper... Some good stuff on earthing.
I probably will get GN8 eventually, but probably by the time I have finished Sparky Ninja's resources a new edition will be out.
What I am really interested in regarding earthing & I suspect not covered by GN8, is how to go about fitting an earthing mat when I have my drive done that will help me in future to use my Solar power off-grid ("Islanding"). I gather from Sparky that proposed standards talk about earthing mats for new builds, e.g adding them to foundations, but no guidance on retro-fitting.
This whole area of installing (or retro fitting) earth mats/rods etc is surprisingly not as well discussed as it could be. There are options out there that could be explored like the kilometers of disconnected metallic services in urban areas already in situ that could be "reactivated" for earthing purposes
 
TT and PME joined happily together.
Broken PEN upstream of yer supply with Mrs Jones at number 42 having a shower and Mr Smith cooking the Sunday roast at 48.
Your point highlights nicely the variables that come in to play during an open PEN FAULT.
Every buggers supply load see's yer poor old Rod as a brightly shining light is seen by moths.
Are you referring here to the standard earth rod?
Best keep em separate, Mind you if its a nice wooden floored shed with no bonding needs even the swa glanded properly will often be a good enough cpc for extending yer TN-C-S arrangement.
Agreed. The construction of the shed is a major fact in the degree
of potential danger under open PEN fault
 
Never used a twig for TT if thats to be known as a standard rod. Hate the bloomin things. So always a substantial rod which of course adds to the reasoning regarding keeping the two earthing arrangements separate. The brighter the light the more moths you attract. Thing is there may well be parallel earth paths upstream but with water and gas arrangements turning to pvc I still reckon the rods going to be a favourite. As said use one or The other but not both. Each system will do the job if installed properly.
 
Never used a twig for TT if thats to be known as a standard rod. Hate the bloomin things.
So do I. Am obliged over here (ROI) to install them with every new install and rewire (our supply system is TNC-S). Always terrified of hitting underground pipes/services
So always a substantial rod which of course adds to the reasoning regarding keeping the two earthing arrangements separate. The brighter the light the more moths you attract.
Do I conclude from this that you feel your earth rod can be a potential danger under open PEN?
Thing is there may well be parallel earth paths upstream but with water and gas arrangements turning to pvc I still reckon the rods going to be a favourite. As said use one or The other but not both. Each system will do the job if installed properly.
Same question as above?
 
So do I. Am obliged over here (ROI) to install them with every new install and rewire (our supply system is TNC-S). Always terrified of hitting underground pipes/services

Do I conclude from this that you feel your earth rod can be a potential danger under open PEN?

Same question as above?
I feel if you dont combine TNC-S with TT you dont need to consider the scenarios of what can potentially happen if an open PEN situation ever developed. A floating voltage suddenly has a return path with unknown currents introduced and limited by the resistance of maybe just the rod maybe not. Why would you allow for that scenario to happen. I prefer not to, its just me. ?
 
You could have the same problem though with a metallic service pipe that’s bonded back to the MET.
If compliant the bonding would be suitably sized for TNC-S and back to the MET, this would also be within the equipotential bonding zone, so not the same issues.
With an out building using a TT system where a TN-C-S earthing has been extended beyond the bonding zone and effectively connected as a combined earth with the Rod. Your into a different scenario, if the PEN is lost downstream.
(Referring to the comments that have gone before on this thread).
So if your extending the PME then you install to that. If your going for TT then that's ok.
But choose one or the other not both. There's really no point.
When we did the installations for petrol stations back in my younger days. PME was not allowed.
TT or TN-S yes but not TN-C-S.
That's it !! off to bed, stay safe guys. ?
 
TT and PME joined happily together.
Broken PEN upstream of yer supply with Mrs Jones at number 42 having a shower and Mr Smith cooking the Sunday roast at 48. Every buggers supply load see's yer poor old Rod as a brightly shining light is seen by moths. Best keep em separate, Mind you if its a nice wooden floored shed with no bonding needs even the swa glanded properly will often be a good enough cpc for extending yer TN-C-S arrangement.
Thanks for sharing that thought provoking response.
 
Would it not be better and easier to install a pen fault device as they do for EV?
like a Garo G6EV40PME Consumer Unit, MCU Type A RCBO & PME Fault, EV Charger Compatible
 

Reply to Exporting Pme in the Electrician Resources and Downloads area at ElectriciansForums.net

Similar threads

Lou submitted a new resource: Flonidan SMETS2 Gas Meter User Instruction Manual - The instruction manual for the Flonidan SMETS2 Gas Meter Read...
Replies
0
Views
536
Lou submitted a new resource: User Manual for Aclara SMETS2 Three Phase Meter - User Manual for Aclara SMETS2 Three Phase Meter Read more about...
Replies
0
Views
918

Search Electricans Forums by Tags

Tags Cloud - Most Used Words - Use them to search for topics

110v 12v 17th 17th edition 18th 18th edition 2 way 2330 2365 2391 240v 3 phase 6mm access account across adding additional advice advise after again alarm alarms always am2 amendment amp another answer anybody anyone anything appliance appliances application apply apprentice apprenticeship approved area arial armoured around assesment assessment attach aus ausie elec available basic bathroom batteries battery because become becoming becsa before being bell best better between black block blowing board boards boiler bonding book books bosch box boxes brand breaker breakers british bs7671 bsi build builder building bulb bulbs business button c&g cable cable size cables calculation calibration camera can't canada car caravan card career cctv ceiling central central heating cert certificate certificates certification certs certsure change changes changing charge charger charging cheap check cheers christmas circuit circuits clamp class code codes college combi coming commercial companies company competent complete condition conductor conductors conduit confused connect connected connecting connection connections connector connectors consumer consumer unit contact contactor content continuity contract contractor control controller conversion cooker copper core correct cost council couple course courses cover cpc cps crabtree cupboard current customer customers dead deal degrees demand design details detector device dewalt diagram difference different dimmer dimmer switch dimmers distribution diversity diy dno doing domestic domestic installer don't door double downlight downlighters downlights drill driver earth earth rod earthing east economy economy 7 ecs edition eic eicr elecsa electric electrical electrical installation electrical nvq electrical tools electrical wiring electrical work electrician electricians electricians london electricians mate electricians vans electricity electrics electriians mnchester element email emergency emergency lighting employed energy engineer engineering enough entry equipment essex every everyone exam existing experience extending extension external extra extractor extractor fan fan fans fault fault finding faulty fcu final finding fire fire alarm first fit fitted fitting fittings fixed flat flats flex flickering floor fluke fluorescent for sale forms forums found free fuse fused fused spur fuses garage garden gas generator get getting going great green grid ground gu10 guidance guide guilds hager halogen happy having heat heater heaters heating hello help help please help! hi everyone hnc hob home honeywell hot tub hours house how to ideas immersion impedance improver in london incoming induction industrial industry information infraction inside inspection inspection and testing install installation installations installed installer installers installing insulated insulation insulation resistance insurance interesting intro introduction inverter inverters isolation isolator issue issues jib jib card job jobs joining junction keeps kewtech kit kitchen knowledge lamp lamps large lead leads leakage led length lenny level level 2 level 3 light light switch lighting lighting circuit lights little live load local location loft london long looking looking for work loop low voltage ltd machine main main switch mains maintenance makita manchester manual mate max maximum mcb mcbs mcs media megger member members message metal meter meter tails meters method metrel mft might minor missing mobile module money motor mounted mounting moving multi multifunction multiple murdoch myself napit need help needed needs neutral never new new build new member newbie niceic night no earth north not uk not working notifiable number nvq off offer office old online opinions options other out outbuilding outdoor outlet outlets output outside oven overload panel panels parallel part part p passed pat pat testing people periodic person pfc phase phone pipe pir place plan plastic plate please plug plumbing advice pme point points pole position possible post posts power practical practice price prices pricing private problem problems project property protected protection protective pump pvc qualification qualifications qualified quality query question questions quick quote radial range rated rates rating rcbo rcbo's rcbos rcd rcd tripping rcd's rcds reading readings really recommend recommendations red regarding registered regs regulations relay remote repair replace replacement replacing required requirements resistance results rewire right ring ring final ring main roman roof room rose running safe safety salary sale saying scheme scotland screwfix sds second section security self self employed sensor series service services shed shock short shower simple single single phase site plan size sizing skills sky small smart smoke smoke alarms socket sockets software solar solar panel solar pv someone something sorry source south spark sparks sparky split spur spurs standard start starter starting steel still storage storage heater strange strip students stuff sub main suggestions supplier suppliers supplies supply supply to surge swa switch switched switches switching system systems t&e table tails taking terminal termostat test tested tester testers testing tests thank the forum their thermal thermostat these thing things thinking those though thought thoughts thread three three phase through time timer times tips today too tool tools trade trainee training transformer transformers trip tripped tripping trips trunking trying tt system type under underfloor underfloor heating unit units update upgrade urgent used using value values valve van vehicle video volt drop voltage voltage drop volts wall wanted warning water weeks welcome west what's whats where white wind wire wired wireless wires wiring wiring help within without work working works worth wrong wylex years zone zones

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top