ArgeeIts about time PME issues like this were addressed with safety monitoring devices that cut the supply at the origin should a loss of neutral occur.
Discuss Exporting Pme in the Electrician Resources and Downloads area at ElectriciansForums.net
ArgeeIts about time PME issues like this were addressed with safety monitoring devices that cut the supply at the origin should a loss of neutral occur.
For the vast majority of sheds, if there is an extraneous part it's likely to be the waterpipe. I would be inclined to insert a section of plastic pipe and convert it to "un-extraneous" (is that English?). Less hassle at times, than running out a 10mm earth.As already said, you can extend the PME to the outbuilding if you BOND any extraneous conductive parts adequately.
Car parked next to shed bond it, metal gate bond it, lady walking by with a pram bond it. rubbish me steel toe caps !! bond it ??Metal walls, metal roof , grill floor , all bonded
A figurative red warning flag has been waving over the dangers of the TNC-S supply system for some time now. You do wonder if it will take a high profile incident (hopefully not) to raise awareness to a point where definate steps must follow. That was literally what happened to cause the introduction of rcd,s into mainstream electrical installation work.Its a very poor situation IMHO when we are now looking at the 18th edition of BS7671 with all the regulations contained there in. And we still have a possible situation where the whole lot can become live to the touch, bypass every protective device in the install, and the only way its addressed is to fit oversized bonding and hope the potential victim is wearing thick soled shoes. Its about time PME issues like this were addressed with safety monitoring devices that cut the supply at the origin should a loss of neutral occur.
In the meantime I will stick with my thoughts that extending TNC-S to a wooden outbuilding is fine, TT my preferred option, but I will never use both methods together. Just my preference. Wonder if the 19th edition will come up with something else to fit into your TNC-S compliant, Non combustible, SPD and RCBO filled C/U. its gonna get crowded in there. ?
Manufacturers of EV charging stations are already on the case ?A figurative red warning flag has been waving over the dangers of the TNC-S supply system for some time now. You do wonder if it will take a high profile incident (hopefully not) to raise awareness to a point where definate steps must follow. That was literally what happened to cause the introduction of rcd,s into mainstream electrical installation work.
How can you Code the loss of a PEN connection when no mention of this is made in BS7671. I really don't get people's obsession with PEN losses.The garage supply is nothing more than a glorified extension lead or submain radial supply if you like. Connecting back to the mains position, and its the mains position that's the origin of the supply, and that's where your PME is. Your extending the earthing arrangement yes but not exporting the pme. As far as coding I wouldn't. If that's worthy of a code then our nice new metalclad boards are all C2s if PENs lost.
well one person at least ?I'm glad someone thinks so ?
How can you Code the loss of a PEN connection when no mention of this is made in BS7671. I really don't get people's obsession with PE
Agree coding is a non starter as said (I wouldn't) You cant start coding based on what may happen if PEN is lost. The C2 scenario was just by example of where and how far do you go, and where do you stop. Although why are there now increased sizes in main earthing and bonding conductors where TNC-S is used , maybe there is something in BS7671, maybe in time it will go further. There are a lot of regulations in the 18th that didn't exist in the 14th per say. So just because its not in there doesn't mean it won't be there in future editions. There is a potential danger with a lost PEN. If you were on the receiving end of a 230 volt live conductive part I think you would probably be a little concerned.How can you Code the loss of a PEN connection when no mention of this is made in BS7671. I really don't get people's obsession with PEN losses.
And I think the discussion on this thread comes from a place of concern rather than obsession. EV charge stations are rapidly on the increase, and with PME being most DNO's adopted earthing preference, you are going to see something addressing issues and short comings with the system, be it by way of amendment's or in a future 19th edition, who knows ? WE have RCDs we have RCBO's we have SPD's and soon we may have the edition of lost PEN monitoring devices on TNC-S systems, who knows. We all have our opinions after all, and its great to discuss different view points ??
Because a) it happens, and b) when it does, then the suppliers "earth" terminal is now "live" at anything up to 240V depending on loads on the system.How can you Code the loss of a PEN connection when no mention of this is made in BS7671. I really don't get people's obsession with PEN losses.