Discuss Cooker cable in the UK Electrical Forum area at ElectriciansForums.net
Hi
we are about to re do our kitchen and am looking for information on the hard wireing for the built in cooker as we want to move it! Can I buy new cable and lengthen the cable from the cooker to the wireing point and have the cable running around behind the cabinets? If not how much would it roughly cost to have a new wireing point installed where it needs to be!
Any help would be great
How is the cooker currently wired? Is there an isolation switch, and a box on the wall behind it with a short lead running to the cooker?
Do you know what the circuit protection (MCB or fuse) is? Are we talking a stand along range with electric hob, or just an oven on a plug?
A picture of your consumer unit, the current location and where you want to move it to will probably help give better advice.
Running cabling behind cabinets is certainly possible, though the length of the new circuit may be limited by various factors, such as the rating of the cooker, the size of cable, etc. Any cabling should be properly supported though rather than just slung across the floor as often happens with kitchen fitters....
Unfortunately, there are lots of factors involved in installing a new cooker to the current regulations, which means unless you are confident in working with electrical cables it is probably better to get an electrician to look at it - cooking appliances tend to be high current drains and any issue with loose connections or incorrect wiring has the potential to cause safety problems more than some other circuits.
It may be necessary to upgrade the current protection to meet current regulations, but that will depend on your current consumer unit age and setup.
It may be worth getting a few quotes in person - the price could vary a lot depending on location but I'd have thought it should only take 1-2 hours maximum, if there is no chasing or channeling involved. Hourly rate can vary wildly depending on size of company, but I'd say the usual range is going to be 30-80. Then there would be the cable, the connection box and clips to add on top.
You should be able to get a fixed price quote from a local smaller one man band or smaller company - they are more likely to be wiling to do small jobs like this.
There is an isolation switch above and a hard wire point behind the cooker! I was just wondering if I can buy a long length of cable and wire it back into the same place it’s wired now instead! Only reason is because there would be chaseinf and channeling involved like you said
thanks
you can wire from the cooker outlet, behind the cupboards , or even on the floor underneath. only criteria is that the cable is routed away from where it may suffer damage and is adequately secured. use same size cable (6.0mm or 10.0mm) as already fitted. you can fit a second outlet close to the new cooker position.
Isn't it 2m max. distance between switch and appliance?
We have been over thus so many times!
The only reference to 2metres are in some of those guides for the hard of thinking.
There is no regulation. In fact there is even no regulation that states that there must be an isolation switch on an oven, or other domestic appliance.
Therefore if there is no requirement for a switch then there can not be a stated distance.
I agree that there is no stated regulation that requires an isolation switch for a cooking appliance.
I do, however, not agree with the somewhat derisory assertion that guides are for the hard of thinking.
I can think of many instances where guides have been, at least to some degree, useful in assisting myself and others when faced with a somewhat unclear decision. Not that we should blindly follow guidance, but that it is often useful, and can add dimension and perspective to a particular situation.
In fact, the On Site Guide, along with Guidance Notes 1-8, are produced by some of the very same people that write the regulations. This being so because it would be impossible to incorporate every single scenario in one book of regulations. Therefore, surely, such additional guidance should be welcomed and not dismissed so readily.
We are professional, trained, skilled and instructed people (hopefully!), and much of the training we have received has come from sources other than the Book of Regulations.
No means of isolation for a cooking appliance? That's extremely unusual. What's the reasoning behind that?
The reasoning is that in a domestic single phase installation the double pole means of isolation can be taken to be the main switch in the consumer unit. The regulations would be met, but in many cases, it would be practical to include a more local means of isolation, in other words a cooker isolation switch. However, the regulations do not specifically require a cooker isolation switch to be installed.
That's putting it mildly
Isolating a cooker at a main switch is crazy
Also there'd be an element of risk in relation to emergency , an MCB wouldn't satisfy that imo
Couple of issues here. Firstly I would say that just because the regs don't specifically call for an isolation switch you have to bear in mind that there is a requirement for isolation for maintenance. Using the main switch at the c/u for this is just poor practice. Do you really think it's OK to turn off the whole installation so one appliance can be serviced. This is why the regs and good practice are to be considered together as this is the essence of good installation.
Secondly I would say it's not OK to extend from the cooker outlet point to the new cooker location if the new kitchen layout means that the original connection point is inaccessible - I.e covered by a kitchen unit. Screw terminals are supposed to be accessible for inspection. So hiding this joint behind a kitchen unit would not comply. Better to extend by running a new cable from the cooker isolation switch to the new location.
And I'm also pretty sure the 2m requirement for the isolator is a building regs requirement. I seem to remember reading this in the "electricians guide to the building regs" some years ago. Which reminds me , I'll. have to get an updated copy. Its a really useful book.
because..... in the case of a N-E fault on an appliance, you can unpl ug it for 2 pole isolation. ovens (usually) don't have a plug and so the
Is there no rule to cover that scenario
They usually are versed like something like "not creating an unnecessary nuisance in an installation"
By leaving out the isolator you're making it difficult for the homeowner to clear the N-E fault
When I hear "Cooker" it means ovan and HOB. It's the single most important appliance in the home, in my view, that should always have local isolation... even if the regs don't require it. The hob poses an added danger in the home for kids. Parents appreciate been able to completely protect children from switching the hob on by accident. This is a secondary but important role local isolation plays.Also the newer hobs which have a touch screen instead of knobs can at times be switched on accidently should water splash on the touch screen. It's really handy under those circumstances to have an isolator lose by.
Final thought, the 2 meter rule is ar reg over here.
I completely agree that a cooker/oven/hob should have local isolation, and would always fit one.
I was merely pointing out that there is no specific requirement for it to be installed.
The guides convey to the "hard of thinking" what the engineers and competent electricians amongst us have worked out for themselves. They may not be regulations, but should be followed unless you can provide good reasons not to.
Reply to Cooker cable in the UK Electrical Forum area at ElectriciansForums.net
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
A house we have just re-wired has one of these cooker points, Trouble is the kitchen wasn't supposed to have been touched by any trade but...
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...