I think you'll find they should go into the bottom of the main switch, otherwise it'll still be live when you turn the main switch off ?
Yes I misread the opening post I thought he was referring to the supply conductors.
A quick search of the usual suppliers are not throwing up ready-to-roll dual RCD link leads with the two lives in one dual ferrule (as you get with a new populated board) only split load kits with 2 Neutral links and 1 Live link.
If finances permit it I'd still cut my losses and go for RCBO's though - much easier!
If you need to make what you have work, options as I see it are:
a) get virtually any 2nd hand dual RCD CU from ebay and steal the link cables. (around £20) This is probably the cheapest way out of the mess, nasty as it is.
b) get a normal split load kit (£15), a ferrule crimper and bootlace ferrules (£10-£30) chop up the live to create a short lead and a longer lead and put new bootlace ferrules on the ends, thus creating two leads with the same ferrule on one end of them. Hopefully they would fit in the main switch terminal side by side. Otherwise you can get dual bootlace ferrules to take two cables but they aren't cheap.
(I really would go for the RCBO's if at all possible!)
As luck would have it, I just fitted a BG board that the customer had supplied.
Populated split RCD board, 10 way (5+5)
You can just about see how the internal connections are made.
Note the ferrules crimped onto the ends of the internal links.
A couple of issues. The busbar needs cut. Comes as a 15 way and needs to be 2x 6… but as you can see here, the RCDs are physically deeper than the MCBs, so the bus at sits at a slight downhill slant.
This in turn gives all the breakers a slant and it’s near impossible to get the cover back on.
Secondly, one of the 16A MCBs is faulty, doesn’t click on.
Third. The 35mm knockout for a tails gland is below the RCD. Would have made sense to put it on the right where there’s plenty space.
That is a good thing, as you might want to shuffle the loads around, but...
<= this is absolute crap!
FFS we get told in the regs to only use the manufacturer-approved parts so they fit properly, etc, and then we have examples that are pretty much "meh, it goes in at a push"
I'm unlikely to be fitting domestic CU but this has been very informative as a reason not to go with ones of these.
the reason the busbars slant is if you push them too far into the MCBs. i never had any trouble with BG.
Just me. I like to push the busbar as far up as I can, thinking the terminal gets the best grip. I suppose I could set it directly horizontal.
Also, might be the fact the CU is fitted tight in a corner, high up at the ceiling and I was tightening with the wrong hand… made everything slant.
Putting the lid on, kept hitting the RCD button
Not a bad design overall the dual RCD board
DP main isolation
All circuits RCD protected
Overcurrent protection provided by dno
The lighting on shared rcds would be the only issue with it imo
I was moaning about this very morning regarding the location of the 30mm knockout, you have to assume that it’s not designed by sparks ?