The new issue that @Mjward has seems to be at least two breaks in the CPC or no CPC at the CU, as there is no earth at some or all socket outlets on an RFC. Because it is a ring, a single loose terminal other than at the CU should only affect one socket-outlet at most. The wander-lead tests will be revealing.
 
The OP @Haphazard81 was last seen 5 months ago, never returned after asking a question.

The new issue that @Mjward has seems to be at least two breaks in the CPC or no CPC at the CU, as there is no earth at some or all socket outlets on an RFC. Because it is a ring, a single loose terminal other than at the CU should only affect one socket-outlet at most. The wander-lead tests will be revealing.
The thread update notification was caught in spam.
My local store didn't have stock of the wander leads on the weekend but I used the time to change a few more of the sockets and map circuit routes which has me flummoxed in one particular room which has far as a can tell has either migrated to a radial setup or has spurs off of spurs. I am hoping herein lies the issue and will spend today mapping out where the wires are going. In the interim, I changed all the sockets in the room, a few loose earths but with new sockets in (and tight cpc fittings), the earth fault remained so post mapping, I suspect the wander-lead will be required to properly diagnose.
 
Completed mapping of entire circuit. Changed all sockets, a few had loose connections but broadly everything was where it should be. Socket tester still showing earth fault. Have identified one shocker of a connection below, hoping it this causing the fault. Failing that, will have to check CU (off) for earth connection and then wander.

20211005_140908.jpg
 
Unfortunately even putting the wires that were taped together into a junction box didn't solve the issue. Given I've mapped the entire circuit, changed all sockets, checked all junction boxes, the earth issue must lie at the CU. I am comfortable with most domestic electrics but won't touch a CU...even if it's off. Time to call the professionals. Shout if anyone is in West Yorkshire and can spare a couple hours (paid of course!) otherwise will check the local classifieds.
 
Unfortunately even putting the wires that were taped together into a junction box didn't solve the issue. Given I've mapped the entire circuit, changed all sockets, checked all junction boxes, the earth issue must lie at the CU. I am comfortable with most domestic electrics but won't touch a CU...even if it's off. Time to call the professionals. Shout if anyone is in West Yorkshire and can spare a couple hours (paid of course!) otherwise will check the local classifieds.
Whereabouts in West Yorkshire are you located?
 
Just outside Hebden Bridge. Could also do with CU upgrade (to Hager with 30A RCBOs) at the same time
is that anywhere near to Leeds. Glennsparks is in Leeds and he's a top man. NICEIC approved contractor.
 