Had to close the bus section on a large MCC panel.
So close the BS and knock off No.1 incoming and No.1 control supply cubicle as the BS also paralleled the control supply, sounds simple. By the time I’d turned off No.1 incomer to the panel and then walked to No.1 control cubical the control wiring was well ablaze.
Result major shut down. Turns out that when the panel had been built the control neutral/earth connections for both transformers had been missed out. There was a neutral/earth fault on one side of the board and live/earth fault on the other.
It turned out I was the first person to operate the bus section in the 26 years the panel had been in use.
 
In the early merlin gerin industrial boards the 3ph busbars linking the mcb's to the main switch were insulated from the front aspect only but they were exposed if you went behind them in the space usually available to run your cables through, i was pushing a 6mm cable through this space an the L3 busbar must have scraped the insulation off as it turned into a blue fire ball blasting through every gap in the main switch cover, it took out the 160amp front enders and when i open the switch up it had got so intense it had melted the wire to all 3 phases.
It was 15yrs ago i learnt a not so obvious lesson and even rang melin to point out this risk, there next generation board was thus fully insulated on linking busbars.
I also know you should switch off dist board when working in it, but who does that to add a circuit even nowadays.
 
Had a phone call to say that the cooker had caught fire and the helpful decorator had turned the whole house off at the main switch. Turns out mr helpful had put a pile of dust sheets on the hob and accidentally turned it on.

so come on why do you ask??
 
Not caused by anything i done !!!!! but helping a client that has just had a fire and i mean fire. freezer compresor caught fire, Nice new restaurant only open 3 days totally buggered atm estimated damage 55,000 euros ffs and counting
 
Right im going to mention this as i feel its important , We recently had a serious house fire , destroyed the house and very sadly infact heart breaking 2 young boys aged 6 and 11 together with their mum lost thier lives , i knew the family such nice boys , this week was the inquest , the cause of the fire was a freezer , why did they die , and what could have saved them , SMOKE Detectors they didnt have them , as sparks , when you do you calls , check the smoke detectors , and insist they have them put in if they dont , i always test the Smokes battery or mains when i do a PIR , or house call , i even put in new batteries FOC , because doing this takes seconds and at the end of the day you may well save some ones life...Daily Post North Wales - News - North Wales News - Policewoman and ...
 
Right im going to mention this as i feel its important , We recently had a serious house fire , destroyed the house and very sadly infact heart breaking 2 young boys aged 6 and 11 together with their mum lost thier lives , i knew the family such nice boys , this week was the inquest , the cause of the fire was a freezer , why did they die , and what could have saved them , SMOKE Detectors they didnt have them , as sparks , when you do you calls , check the smoke detectors , and insist they have them put in if they dont , i always test the Smokes battery or mains when i do a PIR , or house call , i even put in new batteries FOC , because doing this takes seconds and at the end of the day you may well save some ones life...Daily Post North Wales - News - North Wales News - Policewoman and ...

i know where you ar coming from nick. when i was 10 a house went up a few doors up from us.two young children died and we heard them screaming, never forget things like that. i always have fitted them as part of a rewire . never have asked if they wanted them. our local fire station are great with handing out free smokes so if always make a point of giving the number out to people who don`t have them.
 
Yes about 27 years ago when I was a second year apprentice, cocked up a joint in an attic which was then was covered in insulation, lots of smoke not exactly a fire. Learnt a lesson though. I am now paranoid about loose terminals, installation methods etc.
 
i very nearly caught on fire when i was an apprentice. 14 odd years ago i had only been in the job for a couple of months if that. had no idea what i was doing my boss thought he would give me a good job to do

this invloved removing the insulation tape, individually wrapped aroung the mcb pins on a 3 phase dist board, because he didnt have any blanks when he fitted it a few days before. yes the board was live and he gave me a pair of side cutters to do it and didnt mention anything about it being dangerous. within less than a minute i had shorted out 2 phases with the side cutters right in fron of me. it looked like a firwork going off in front of me.

think i was very lucky not to get hurt. Once i had learnt more about electrickary i realised what a frickin stupid thing to get someone to do especially a new trainee.
 
worked for a guy once that was having a 100k public liable claim being made against him by a customer for a fire. One of his lads was rewiring the garage, he didn't manage to finish in a day so left his tools etc on the job ,all the electrics were safe power was on, only the lighting was de energised . Anyway half the house went up and it was found that the kiln in the garage had some old newspapers on top of it, someone had plugged it in and basically it was the customers word against his lads as to who had plugged it in, they found in favour of the customer bit harsh me thinks should have been a 50\50 insurance split but they claimed it all on his. I've worked with the guy and he is a good sparky but it's shot his confidence to bits.
 
lol...!

started a non electrical fire in my early days of apprenticeship on the nuke subs!! had a stubborn nut on a flange and well after nearly a whole day of trying to free it WE (me and my section leader) decided to heat it up with a Acetylne Welder and burn it off!! any way less than 30 seconds later the pipe lagging was well ablaze and me looking at my gaffer for the job dived for the nearest Foam Extingushers to put it out!! then lesson learnt ...!! NO away we went for a second time with a bit more care and started the same fire AGAIN!!! we gave up after than one!!
 
Had an incident a few years back which wasn't to do with us, though we kept getting the blame for the Fire alarm going off. In turn this was setting off a LUL station alarm, evacuating it, and costing, well, quite a bit. Our system was in a substation.

Upshot, was we put in CCTV either side of the detector that kept alarming, just to see if we could see any reason for it. And did we. Sadly, I can't find the footage now.

There as a bloody great open DC breaker - 5kA - and one of the last open ones. What was happening, was they'd hit a peak demand on the line it was supplying, and the breaker was actually tripping nearer 8.5kA - and boy, when it went..........bang, wasn't in it. But it was arcing something rotten too, as they do when they go, and that was catching alight all the dust and stuff which had collected around the top of the breaker.

It was like watching a supernova on the CCTV.

What I found interesting was that after months, and months of blaming the company I was working for, denying that the breakers had anything to do with it, or that the problem was anything other than the Fire Alarm, that breaker was changed in two days flat - for a 10kA closed breaker......

Two things - (1) - Fire alarms do their job! (2) There's a good case for unmanned systems having CCTV integrated, for safety and education.
 