Any issues with wiring lighting in 4core flex rather than 3core and earth?
Approximately 50 LED panels to wire all fitting into a suspended ceiling.
I know some lighting design/manufacturing companies sell plug and play style fittings and wiring which I think may be H05.
Is there a great deal of different in the properties of standard rubber flex (not sure of the correct cable ref for this) and H05?
Can both be used or stick to H07?
I think H05 is a bit of an overkill, a standard general purpose pvc/pvc flexible cable would suffice and be cheaper too.
H05 is (or I thought) for external (wet) areas and also resistant to oils and the like.
How is the cable being installed?
This sounds like it would lend itself to a system like the multiway rock-rose (Klick I think is the proper name) boxes. Depending on exactly how it is all being installed I would normally go for 3C&E flexshield as my cable of choice for such an install if it needs an insulated and sheathed cable.
Otherwise the old school way is steel trunking/conduit and rock roses. This is my preferred method if its being wired before the ceiling grid is installed and there isn't a ridiculous time pressure.
H05 is a general designation that covers many types of sheath/insulation including PVC, EPDM, rubber & more
Nearly every refurb shop fit that I have worked on the wiring is LSOH flat cable for the fixed wiring and just normal flex to the lights with some white FP thrown in for good measure
Suspended ceiling already in place.
Customer wanting to save costs and not interested in paying for marshaling boxes etc.
Good old fashioned in and out using wago accessories has been agreed. Definitely not my preferred method or first choice but can't see any reason why this isn't acceptable for current regs and saves the customer a few quid. I think the marshaling boxes are approximately £80-100 each so saving £400-500 on boxes alone. Add in the cost of the Klik plugs and pre-made leads etc, could be saving £600-750.... mad.
Whether it is H03, H05 or H07 has nothing to with its suitability for a particular area, it is the standard it complies with and voltage rating of the insulation.
Standard singles are an H07 cable and they certainly aren't suitable for being outside of a conduit, let alone outdoors.
H = meets harmonised standards.
Voltage ratings are (Uo/U) :
01 = 100/100V
03 = 300/300V
05 = 300/500V rating
07 = 450/750V
It's the letters after this which tell you what tbe insulation and sheath (if any) are made of (therefore the type of environment it is suitable for, temperature resistance etc), type of conductors (F = flexible for example)
So
H05-VVF is PVC/PVC flex
H05-RRF is rubber/rubber flex
H07-RNF is rubber/neoprene (IIRC) flex, which is the generally accepted stardard for a heavy duty, weather resistant, oil resistant etc etc flex.
I'm not sure if it is still true but the regulations used to suggest H07-RNF as a benchmark standard for flex suitable for general purpose permanent installation.
Ah yes, the good old customer-led cheap design without thought for ease of future modification, maintainence, fault finding or health and safety.
How are the cable being installed? Are you proposing flex for the entire installation?
01 = 100/100V
03 = 300/300V
07 = 450/750V
So
Sounds like H07-RNF is what I'll be needing then. Thanks for that.
Wouldn't say it was customer-led. The customer was given acceptable options and decided for themselves what they could afford. I don't see an issue with that.
Whats the health and safety aspect of the proposed work which concerns you?
Everyone's had 2p put in their box tonight it seems! 😂
Metal fixing band above the ceiling as containment. Again, cost cutting. Usually fit basket tray but this is £10-£15 per length as opposed to a £5 roll of hole-band!
IAmSparkytus!,
nicebutdim,