Recently my RCCB keeps keeps tripping intermittently. It can happen between several hours to few days when a trip will occur. During the trips, no additional appliances were switched on or being used. There are times when it simply trips in middle of night when most appliances are not running.
There are also times when the trips can happen successively a few times in a minute but was able to recover after several resets.
So far am able to reset the RCCB all the time.
On few occasions, one of my MCBs also tripped & this helped me to suspect the issue could be isolated to one of my rooms. However in most cases only the RCCB trips, hopefully the occasional MCB tripping is not leading me to a wild goose chase.
With this, I had to switch off each devices in this room connected to the tripped MCB & monitor several days if trips been resolved.
Reading few blogs, MCB trips could be due to faulty appliance or overloading.
In this room, I have 3 PCs, 1 router & 3 handphone chargers plugged in into 2 socket outlets with 2 multiple sockets extension. I had this connection for several months w/o power trips which is why I am not suspecting overloading here.
In some instances of power trips during the nights, PCs & chargers are not in used, although power was not switched off for the chargers. Only the router is turned on all this time.
if faulty appliance, I would expect the trips would be almost immediate & not so intermittent.
Was hoping to find out any quick method to determine which of this is the cause of the intermittent trips other than isolating one each time & monitor several days.
Another suspect could be the RCCB itself although this would cost me to purchase a new one or engage a licensed electrician to fix it.
If the MCB is tripping then you potentially have quite a serious fault. I would definitely get an electrician in to look at this. Someone with the proper test equipment will be able to narrow things down.
Sounds like the MCB is tripping as well though
This was my initial suspect too as the fridge is the only high powered appliance turned on all the time. However the occasional trip on one of my MCB is not on the circuit of the kitchen. Is there a way to check whether the fridge is the culprit, it is 10yr old & I do see some sweating outside the freezer compartment, but this has been like that for past year w/o power trips.
Isolating the fridge is not a choice since I need to use it 24/7.
The intermittent trips makes it so difficult to pinpoint where exactly is the cause.
Can you use an extension cable and plug the fridge into a socket on a different circuit?
The intermittent trips still occurring, sometimes more than 12hrs apart w/o any additional appliances being used, with this am more likely now suspecting to be the fridge which is the only heavy loaded appliance operational all this while.
Only puzzling thing how it can be this intermittent as in several hours apart on the trips. Most of the trips also seem to happen during late into the wee hours, though day time does trip too.
Am thinking of getting the external power socket with a RCD, 13A Gfci Leakage Protection Plug on it to connect this to the fridge, so that if it is the cause, it will only trip this RCD instead of the entire house RCCB. This device is affordable instead of replacing entire fridge.
Prior to my new fridge which is a wait of 5 days, any idea how to overcome the regular trips during the fridge defrost heaters acting up? My trips are now abt ~11-12hrs apart which means the current defrost freq set is likely 12hrs. I was contemplating to turn the fridge power off for 60mins during those defrost cycles periods, whether this is advisable.
I was still hoping whether the external RCD socket will work though, so it only trips the fridge instead of entire house.
I’m afraid it’s unlikely an extra RCD socket will not also trip the upstream device too.
There isn’t much you can do that is practical in the meantime.
Does your cooker switch have a socket on it? An extension lead from that might be a temporary workaround.
Getting the normal leakage current measured or the RCD ramp tested would normally be the first course of action before replacing appliances. Or did you prove beyond doubt it’s the fridge?
Nope, my cooker hob is using gas. It is due to the frequent trips & the pattern that I have tracked which is very clearly that the trips occur around the ~12hrs intervals which I highly suspect its the fridge, which I read around that it has defrost times set at various intervals, some can be as long as 12hrs. My fridge is also >10 years old & some sweating seen at external freezer door, its about time to change anyways. Just that meantime, wat probable steps to take to prevent entire house to trip during the ~12hrs intervals.