A
Acidifoant
Hello guys, I have a small problem assigning the correct codes for some visual faults. I am still confused and looking forward to find a good answer.
This is for examination only. It is to be 17'th edition compliant(not 18th).
So we have the following faults and observations requiring a fault code:
1: 13A Socket outlet >ring circuit>Reversed polarity between L and N at the socket.
2: same ring circuit>incorrect electrical connection at the spur(one leg connected into IN terminals and one leg into OUT terminal)instead of both into IN terminal (open ring). the spur is switched and fused.
3: 16A C socket> L2 and L3 reversed polarity at the socket terminals.
4: 16A C socket>unsatisfactory electrical connection>swa armour used as CPC>Armour loose into gland.
5: bonding to gas and water using a single cable connected with plastic covered clamps with no (safety connection-do not remove) notice.
6: undersized earthing conductor(10mm) from distributor to main earth bar for 25mm incoming tails. (it should be 16)
7: incoming tails(3 phase) entering the board(metallic enclosure) through a hole approx 35mm . double insulated tails. no support ,no gland, loose, no mechanical protection around the hole(sharp edge) straight into main isolator.
8: 3 phase incoming tails double sheated with grey (outer sheat) for all tails and inner sheat with blue for neutral and brown for all phases. no colour indentification, no number or label for idenification of each phase.
9: boiler cable protected by a 20A B type mcb and terminated into OUT connectors of the switched spur and the flexi cable into IN connectors.(the board schedule shows 16A breaker). 1.5mm, 1mmCPC twin and earth cable.
10: reversed polarity on a luminaire.
11: as per point 9, a departure from the installation circuit schedule when the actual MCB is different than the one stated in the board Schedule.
Any help would be greatly appreciated.
George
George