Hi all
So had some issues lately related to high current fittings .. dp switches mostly.
A number of electric boilers of various ratings .. from 7kw on up burning out their isolators .. the last one this week was a 7.5kw electric boiler running on a 6mm t&e cable 4m long from a 32A MCB .. 50A dp switch isolator.
No sign of cable overheating at the boiler (even though the terminal block is by the output pipe) . No sign of cable over heating at the consumer unit.. no tripping of the 32A mcb ..
So I understand the the cable is rated to carry over the 32.5 ish A which is max load .. mostly the boiler is modulating and no using anywhere near full power.
Now i know that there are issues with various 13A sockets that are not rated to supply 13A continuously 24 7 .. and these have caused problems with things like car charging.. we use all Hager fittings which I believe are all rated for continuous duty of there rated current... but many manufacturers sockets are not .. my question is are many dp switches and other fittings not rated for continuous duty at their started rating.. and this is causing them to fail at much lower loadings .. and if so how do I find out the continuous duty rating of such fittings.. I believe they should be published ..but a quick search tonight I can't turn up any ratings.
I know at the installation stage it's easy to over rate these things .. which I guess is why the installer for the 7.5kw boiler fitted a 50A dp switch .. but it still failed.
All thoughts greatfully accepted
Ta
Vito
Mmm.. but modern loads are getting bigger ..and more continuous.. and no one will win any jobs using fittings like this .. without being able to demonstrate a reason why .. such as continuous duty ratings .. but is there any such thing.?
As a general rule, I tend to over spec any equipment that will be run for long durations by at least 50%
Hi James ..
Yes I agree .. this was a 50A dp switch on a 32A circuit..
But any ideas where I can find rated duty info for manufacturers fittings so I can tell what to fit.?
An isolator should be rated for 100% duty.
however, over spec and it will last longer.
If the 50A switch was only suitable for intermittent use it would be stated as such.
I refer again to some manufacturers 13A socket outlets that are not rated for 13A continuous .. and some are .. such sockets intended for use charging cars for instance should be rated for 13A continuous.. .. does this apply to other fittings?
Have you established what has caused the failure of the switches?
Do you have any clear pictures of the failed items, preferably with the cable still connected?
If the failure is due to the switch not being suitably rated then it will likely be the switch contacts themselves inside the unit which are failing.
If it is however not down to the switch itself but maybe a poor cable termination, which is far more common, then there will be a lot of obvious burning of the cable at the terminal.
What type of cable is fitted between the isolator and the boiler?
How many installations has this happened on?
Has it been multiple times at the same installation?
Were they all connected by the same contractor?
Could they or a supllier have bought a job lot of isolators which just happened to be from a faulty batch?
Have any of the failed isolators been returned to Hager for investigation?
Hi Davesparks
The installations are varied and not linked by type or installer.. but by loads such as electric boilers ..Hi current continuous loads .. that seem to be installed correctly..
The most recent that I'm referring to as an example was actually a schneider electric 50A dp switch that had failed ..it was welded in the on position both live & neutral supply and load side cables overheated for about 25mm from the terminal.. terminals seemed good and tight but its hard to be sure at this point.
No cable thermal damage at the boiler end or the consumer unit end ..no tripping of the 32A mcb .
I was using hager as an example due to the stated duty rating of there 13A sockets being for continuous load 24-7 .. and wondering if this applys to other fittings like dp switches and isolators.
But we have seen the issue with various brands of dp switches.. we all expect cheap ones to fail .. but they all seem suspect..pretty much always on a circuit rated less than the switch that has failed.. 40 / 50A dp switches on 32A /40A circuits.
So again I want to know is there a duty rating and if so where can I find it so I can spec appropriately.
Unfortunately I don't know the answer to that, I've never tried to use that type of isolator for a true high current load.
I would be considering a good quality rotary isolator if it is going to be located somewhere where an ugly ioskator isn't going to be a problem. And as far as good quality rotary isolators go I'd use Craig and Derricot.