Fuses are old technology and cheap by comparison, but they naturally have a "delay" in how the wire heats up, and they offer exceptionally good energy-limiting. So if you really don't expect them to be blown/tripped, they are a very good alternative and will just sit there for decade after decade after decade, and still work if called upon.
Hence my suggestion of a small Ryefield!
If it is feeding sub-mains so 5s disconnect and all 63A or above it makes a lot of sense.
But I think there is at least on 3P load for a heat-pump, that would be better served by some 3P MCB or similar so on fault all phases go down. Still a DIN box and MCB from a set of fuses is still quite a viable option.
Thing is, it's never just a heat pump, is it. It's some local sockets, a light or two...... so my choice would be to supply a small 4way 3ph board from said Ryefield. If you're building a plant room, build a plant room! Not some abomination of tails spaghetti.
Not sure if I’ve understood this properly, but it appears to have parallels with my own installation. I highly dislike the idea of feeding SP sub-mains from a TP board, unless for very small local loads - which are not likely to increase in the future - like, maybe, a garden shed. I would never even consider a single phase 80A sub main.
For anything else I run 4 (or 5) core SWA to additional TPN distribution boards. Then you have the ability to properly balance loads between the phases, and to run any future 3P loads.
And it looks a whole lot better. 😏
I buy Hager 3P DBs when they come up on EBay, and populate them with Hager RCBOs from the same source. So it doesn’t even cost much.
OP: are these new 3-core runs long, buried, or otherwise non-negotiable?