As above plus
grey should be used a N with blue sheath.
armour is not earthed.
Perfectly acceptable to use black as the neutral conductor providing it is correctly identified.
The supply is using black as neutral and grey as earth. I would seriously question the competence of someone who cannot even get that correct.
Things wrong in this picture;
1. Basic insulation showing (meter cabs are not considered suitable enclosures) interestingly site applied insulation (heat shrink) is no longer classed as suitable in an application like this either.
2. Black being used as the N (personally don’t see a problem with it and I’m not aware of any regs which explicitly state black cannot be used as a neutral) but the NICEIC ran a campaign to “de-neutralise” the black. Bigger problem IMO is no sleeving to identify it as a neutral.
3. Difficult to tell from just a photo but that doesn’t appear to be a 25mm SWA and the cut-out says 100A fuse fitted. So OCPD is too large for cable.
4. Whilst not a 7671 reg most DNOs/DSOs specify that meter tails can only use the cutout fuse as an OCPD where the tails are less than 3 metres.
5. SWA braid is not earthed.
6. SWA is not terminated correctly.
Or not as the case might be.
Think there was a debate previously on the forum as to whether a meter box is considered an enclosure because it is lockable (don't laugh) and a key is needed!
According to NICEIC and Select it isn’t classed as a suitable enclosure as non-skilled persons access the enclosure regularly/to read the meter etc.
Glanding the cable to a metal fused-switch like the Wylex ones would have been far better, then double insulated tails to the meter.
It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?
Morcombe and Wise, Two Ronnies???
Might I direct you fine gentlemen to another thread….
It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?View attachment 112405
Didn’t even see that dent/damage.
Looking at the size of the damage, it could have possibly been some sought of over tightened Earth strap? (But why)? I’ve run out of idea.
Merry Xmas
The earth tag does not match the template laid out in BS7671.
The text should read,
"Safety Electrical Connection, Do Not Remove"
Not,
"Safety Electrical Earth, Do Not Remove"
I'd also argue the Hepworth branding should not be there and the standard Earth pictogram is not used.
Pedantic, yes, but it is a noncompliance.
mmm! not so sure Id agree it as a non-compliance, Isn't there a passage in the regs that says "alternative 'systems/methods' etc shall not be precluded as long as safety isn't impaired" (or something like that as I Don't have regs book to hand )?
Alternative wording/pictograms hardly impairs safety and message is clear enough!
OK so I was clutching at straws but it is the kind of thing examiners include solely to stop people getting full marks.
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.
The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.
With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….
They replaced meter tails with SWA making the MET remote.
We don't know how the swa terminates or if it is downstream fused.
A bit of a botch, whatever way you look at it.
A Spn fused connection unit would have been the way, but even then could cause a moan from the dno for using the meter cabinet.
I'd suggest the opposite.
Suppose you lose the connection between MET and CU ? Your bonding is now probably via the 0.75mm flex to the boiler. By running a connection direct from service head to CU and also taking your bonding cables to the CU, you've eliminated two connections and reduced the risk of incomplete/ineffective bonding.
Reply to Can anyone tell me what is wrong/incorrect. in the UK Electrical Forum area at ElectriciansForums.net
I went to see ABBA Voyage recently and the show was just mind blowing, staging, lighting, sound - just everything! I was talking about it last...
Right or wrong please? , if wrong, what needs to be done to fix it? thanks in advance.