It maybe at the other end.armour is not earthed.
Or not as the case might be.In an enclosure ?
Perfectly acceptable to use black as the neutral conductor providing it is correctly identified.
Blue? looks like Brown to me!black as neutral and blue as a line.
Blue? looks like Brown to me!
Things wrong in this picture;
According to NICEIC and Select it isn’t classed as a suitable enclosure as non-skilled persons access the enclosure regularly/to read the meter etc.Or not as the case might be.
Think there was a debate previously on the forum as to whether a meter box is considered an enclosure because it is lockable (don't laugh) and a key is needed!
Still not done properly though, pretty bad practice earthing the armour from the far end of the circuit.It maybe at the other end.
3x 16m showing on pic.lash up job.Difficult to tell from just a photo but that doesn’t appear to be a 25mm SWA and the cut-out says 100A fuse fitted. So OCPD is too large for cable
I could only muster up 5 issues, but apparently there’s a 6th.!@Penguin are you asking to see if we know or because you want to know?