Jun 3, 2023
116
37
1,203
London UK
Other
If other, please explain
Electrical Assessor
Basic insulation
Or is this a trick question?
As above plus
grey should be used a N with blue sheath.
armour is not earthed.
Perfectly acceptable to use black as the neutral conductor providing it is correctly identified.
No switch fuse then for the feed then.
What is it feeding.
Reactions: pc1966
Reactions: MFS Electrical
In an enclosure ?
Or not as the case might be.
Think there was a debate previously on the forum as to whether a meter box is considered an enclosure because it is lockable (don't laugh) and a key is needed!
The supply is using black as neutral and grey as earth. I would seriously question the competence of someone who cannot even get that correct.
Probably 16mm comparing physical size with the Blue tail and the G/Y but not necessarily incorrect.
Reactions: pc1966
Things wrong in this picture;
1. Basic insulation showing (meter cabs are not considered suitable enclosures) interestingly site applied insulation (heat shrink) is no longer classed as suitable in an application like this either.
2. Black being used as the N (personally don’t see a problem with it and I’m not aware of any regs which explicitly state black cannot be used as a neutral) but the NICEIC ran a campaign to “de-neutralise” the black. Bigger problem IMO is no sleeving to identify it as a neutral.
3. Difficult to tell from just a photo but that doesn’t appear to be a 25mm SWA and the cut-out says 100A fuse fitted. So OCPD is too large for cable.
4. Whilst not a 7671 reg most DNOs/DSOs specify that meter tails can only use the cutout fuse as an OCPD where the tails are less than 3 metres.
5. SWA braid is not earthed.
6. SWA is not terminated correctly.
According to NICEIC and Select it isn’t classed as a suitable enclosure as non-skilled persons access the enclosure regularly/to read the meter etc.
It maybe at the other end.
Still not done properly though, pretty bad practice earthing the armour from the far end of the circuit.
Zs of the braid would be significantly higher.
And installed contrary to manufacturer’s instructions.
Reactions: pc1966
@Penguin are you asking to see if we know or because you want to know?
Reactions: mainline and DPG
3x 16m showing on pic.lash up job.
Seeing with my big eyes.
Reactions: pc1966
I hope we haven’t just done someone’s homework for them…..
  • Funny
Reactions: pc1966 and DPG
Glanding the cable to a metal fused-switch like the Wylex ones would have been far better, then double insulated tails to the meter.
It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?
Reactions: Penguin
I could only muster up 5 issues, but apparently there’s a 6th.!
So I opened up the challenge to you guys.
London UK
Other
Electrical Assessor
Can anyone tell me what is wrong/incorrect.
UK
Penguin,
Simon47,