Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual board or RCBOs. I know there can be issues with Selectivity having an upstream and downstream RCD. One Should really be S type (more expense). Should one 30mA RCD be removed? I am really not bothered which RCD activates as long as one does in event of providing additional protection. Just seems to add to cost replacing one with a simple on/off isolator. I am just concerned neither work.
 
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual board or RCBOs. I know there can be issues with Selectivity having an upstream and downstream RCD. One Should really be S type (more expense). Should one 30mA RCD be removed? I am really not bothered which RCD activates as long as one does in event of providing additional protection. Just seems to add to cost replacing one with a simple on/off isolator. I am just concerned neither work.
I am referring to garage distribution boards fed off main boards
 
Either seek to avoid RCD protection at source or buy a mainswitch board for the garage.

Not sure how you'd justify replacing one RCD in a dual board with a Type S device or removing one RCD entirely.
 
Either seek to avoid RCD protection at source or buy a mainswitch board for the garage.

Not sure how you'd justify replacing one RCD in a dual board with a Type S device or removing one RCD entirely.
What is likely the happen with two 30mA RCDs upstream/downstream. Could you loose all additional protection or will unable to predict which will activate?
 
What is likely the happen with two 30mA RCDs upstream/downstream. Could you loose all additional protection or will unable to predict which will activate?

No selectivity between devices, so in theory either could trip. In reality it's always going to be whichever is most inconvenient - Murphy's Law dictates you'll take out the upstream device and half the house.

From a regulatory perspective the installation would be non-compliant.
 
Ok thanks. I will try and get a wee sub board without RCD device as would be easier than fitting Escos etc and rewiring consumer bits of consumer unit. Thanks for you help mate.
 
When I do a new garage / add power to a garage , I put the rcd in the house and assemble a small main switch board for the garage with what ever MCBs I need in there.
 
Yes that's what I am going to do. Believe it or not it actually more expensive than just buying a complete garage unit - but they all have RCDs. Thanks.
 
Yes that's what I am going to do. Believe it or not it actually more expensive than just buying a complete garage unit - but they all have RCDs. Thanks.
just buy the cheapest garage board , buy a seperate 80a switch and swap it out. in the grand scheme of a job it adds about a tenner to the material cost
 
Are you going to incorporate surge protection into it?
Prob not. It's my own garage. Washing machine, dryer etc, lights etc. But yea know were you coming from prob fact I don't fit one will regret it later Murphy's Law. Actually was looking to see if maybe room in the main consumer. Unit for Type 2 but there is not. If I was getting on I would prefer to protect whole house. Maybe see if it can be done as stand alone enclosure at main consumer unit.. Cheers Jonny
 
You will need RCD protection somewhere is virtually every case. If it is fed via SWA cable so no need for protection on the distribution cable then it makes sense to have just a MCB at the house CU and then RCD and any other MCBs at the garage.

However, if you can't be sure of the sub-main installation then having RCD/RCBO at house and then just MCB at the garage is a better choice.

Two 30mA RCD in series without selectivity is poor design, not enough to worry about on an EICR beyond C3, but not something you should aim to do unless you have a very good reason.

Having said that, having MCB in series or RCBO+MCB will have negligible fault selectivity, even if they are OK on overload due to a 1.6:1 or greater difference in rated current. Again, not good design, but usually an acceptable trade-off if the final circuits in the garage are not critical as done in practically every case.
 