Where is the complicated part?
There isn't one.

433.1 Coordination between conductor and overload protective device
Every circuit shall be designed so that a small overload of long duration is unlikely to occur.

So if you want some electrical work done, call a decent electrician who complies with bs7671.
 
433-01-01 A protective device shall be provided to break any overload current flowing in the circuit conductors before such a current causes a temperature rise detrimental to insulation, joints, terminations or the surroundings of conductors. Every circuit shall be designed so that a small overload of a long duration is unlikely to occur.
 