I need to provide a earth for just 1 light fitting to the shed. There is no earth at the switch but there is a earth bonding for the boiler near by. Will it be ok to spur off this earth/CPC?

Thanks in advance
 
I need to provide a earth for just 1 light fitting to the shed. There is no earth at the switch but there is a earth bonding for the boiler near by. Will it be ok to spur off this earth/CPC?

Thanks in advance
Short answer No

Long Answer

Reg 543.6.1 Where overcurrent protective devices are used for fault protection, the protective conductor shall be incorporated in the same wiring system as the live conductors or in their immediate vicinity.
 
Thanks for the answers. Found an earth in the cable further up. For some reason it had been pulled out!. The cabling is old black and red 1mm2.

I've now connected the outside light circuit here, there are 6 led lights and 1 halogen bulb. The halogen bulb does not light up and all the led lights are dim and flicker I've checked the voltage and it's pretty much 190v which seems to be the same across the other lighting circuits.

Any ideas what will be causing this?