Ok, a totally new one for me. At a new build & the customer was being quoted unbelievable money for SSE to install power into the property as the transformer was so far away from the house. So after back & forths they ended going for getting a white meter box at the bottom of the pole at the end of the field with a meter installed in there & the customer installed their own 70mm SWA (it’s a long run) to the house. I’m not sure what the best & safest way is going to be to get this terminated & fitted at the meter end. Obviously it will be tight for room getting it all in the one box. What is the IP rating for those boxes as well. Anybody
experienced this before?
 
I would say this hasn't been thought out. The cable is going to need circuit protection so you are going to need a switch-fuse and that is not going to fit in a meter box, you really needed an outdoor service pillar.
 
is this a temp job.meter boxes rated at ip66.
Nope this is going to be permanent!
I presume it will be TT then .
Why?
I would say this hasn't been thought out. The cable is going to need circuit protection so you are going to need a switch-fuse and that is not going to fit in a meter box, you really needed an outdoor service pillar.
I had no say or in-put in this, his brother who is an electrical engineer took care of it, only found out about it once the cable was in.
We used a green GRP box.

Just alongside the existing white meter box? Or did you put it all in the one box.
 
I have seen a few like this, The best way is a brick built box with doors and a roof, and a wooden back board big enough for the cut out and meter, a switchfuse and a joint box to transition from the 35mm tails to the 70mm swa. However it sounds like the meter box has already been fitted, so I would fit a switch fuse in the meter box and come out in 35mm swa and do a resin filled straight joint onto the 70 swa underground.
I don't think it has to be TT but, I think I would TT the house and have the submain TNS.
 
Ok, a totally new one for me. At a new build & the customer was being quoted unbelievable money for SSE to install power into the property as the transformer was so far away from the house. So after back & forths they ended going for getting a white meter box at the bottom of the pole at the end of the field with a meter installed in there & the customer installed their own 70mm SWA (it’s a long run) to the house. I’m not sure what the best & safest way is going to be to get this terminated & fitted at the meter end. Obviously it will be tight for room getting it all in the one box. What is the IP rating for those boxes as well. Anybody
experienced this before?

??
 
I have seen a few like this, The best way is a brick built box with doors and a roof, and a wooden back board big enough for the cut out and meter, a switchfuse and a joint box to transition from the 35mm tails to the 70mm swa. However it sounds like the meter box has already been fitted, so I would fit a switch fuse in the meter box and come out in 35mm swa and do a resin filled straight joint onto the 70 swa underground.
I don't think it has to be TT but, I think I would TT the house and have the submain TNS.

Can I ask why you would TT the house & TNS the submain? Like I said this sort of install is new ground to me so any input is helpful.
 