,Hi all,
This is my first post thus up-front apologies for errors or etiquette infringements 😊 Me: I’m retired now, and just a DIYer, always looking to our next project, using local professionals for installation.
I’ve looked through the forum and found similar items but they are not the same hence this post.
The project, we have a solar installation with storage batteries, and IMHO with the increasing possibilities of power cuts, I want to legally and safely use the solar/batteries during any grid outages.
First question; does anyone have user experience/knowledge of the ā€œGEYA W2R 100A ATSā€ shown in the schematic? Chosen purely due to space limitations.
  • I’m considering having one placed between the Smart Meter and Consumer unit, in its own enclosure, and using the Emergency Power Supply output of the grid tied solar inverter as the Back Up supply to the W2R. I have also contacted GEYA and explained the way it is planned to be used including being able to support exported power, and in short, they say its fully compatible and will accept 25mm2 tails.
When in grid power fail mode, the solar installation requires an ā€œislandā€ earth solution in case the DNO earth has been compromised during the outage, that’s if I’ve understood the reg’s correctly (I believe it is 551.4.3.2.1 from BS 7671).
Second question, ā€œMust this earth be run to and connected to the main consumer unit (DB1), or can it be terminated in the garage at the distribution unit (DB2), far easier cable routeing.
  • DB2 is a slave from DB1 and feeds the solar, heat pump and EV charger installations.
I have attached a hand drawn schematic showing the ā€œTo beā€ installation, in a grid power outage condition, hopefully makes sense of the above questions.
Many thanks in advance for any feedback/help on the above questions, it will help me when explaining to the electrician exactly what I'm after and why.
I am no expert on this at all, but have done some limited research on my own behalf and to pick up on one aspect - looking at your diagram (I was interested what I might learn as I have not previously come across this device) I cannot see any reference to a N-E Bond relay as discussed in the "IET Code of Practice on Electrical Energy Storage Systems". I suggest you research this.
A quote from the document that might help:
in systems operating in island mode, the distributor’s neutral-earth link cannot and must not be relied upon, as this is switched out when the live conductors are disconnected.
An installation that operates in island mode therefore requires:
  • a switching mechanism to disconnect live conductors of the installation that are to be powered in island mode from the grid. The IET Code of Practice for Electrical Energy Storage Systems calls this an island mode isolator
  • a switching mechanism to provide a neutral for the island mode The IET Code of Practice for Electrical Energy Storage Systems calls this an N-E bond relay, and
  • a consumer earth electrode. In TT systems, this may be the TT system consumer electrode, if it meets specific technical requirements.
The earthing arrangement of most EESS in island mode, where the installation has a low voltage public supply connection, is therefore always TN-S.
Note: If the N-E bond relay were not present, and the EESS inverter has a permanent connection between neutral and earth, RCDs in the installation would operate, as this would effectively be a neutral to earth fault in the installation.
Note: In installations where PME conditions apply in connected mode, PME conditions continue to apply in island mode. This is because the distributor’s means of earthing remains connected, even though it is not used.
simplified-illustration-of-earthing-and-switch-over-arrangements-in-connected-mode-and-island...webp
In my experience earthing arrangements for use when operating in Island mode are poorly understood in the industry (none of the installers I approached to install my own BESS seemed to understand it). I just have an EPS socket at the moment.
You also need to consider if your system has sufficient grunt to handle the power demands of your house during a power cut.
You may need to limit any switchover to specific circuits.
I will be interested to see any other comments on your post.
Thank you for your comments very useful, unless I have completely misunderstood the reg’s and the island earthing requirements, I think I had only forgotten to show the N-E bonding:-
ā€œI cannot see any reference to a N-E Bond relayā€ – Thank you I had missed the bonding from the drawing, now added to V2 of the schematic 😊 The relay is part and parcel of the GEYA W2R ATS.
ā€œIsland Earthingā€- My interpretation of the reg’s is that I need a new electrode and earth supply (16mm2) installing, I am confidence I have covered the additional earth as show in the bottom right hand of the drawing. That leaves the question on its point of termination, your drawings show it terminating on the maintained loads, that is why I believe it can be terminated on DB2 in the garage, but happy to be proven incorrect.
There are bags of power via the inverter, from the storage and PV panels, the ATS requires a minimum of 3Kw on the Back Up power supply our current inverter is 5Kw, but due an upgrade to 7.5Kw. The solar/storage installation will handle the house, especially as the heat pump and car charger will be shut down, they are the two single most power consumers, c11.5 Kw when both running.
I’ve not yet formally approached any installers so I have no concept of knowledge on the subject hence doing all my homework first.
I look forward to further commentary from all, especially working knowledge of the W2R – it all helps in squaring off the design.
Regarding an Earth electrode, I would recommend a Condudisc. Far superior to an ordinary electrode, both in the earth resistance reading you will get and durability. Although rather more expensive of course.
However, the moment you disconnect the DNO neutral, your inverter's EPS output becomes a floating IT supply. Without a physical bond between Neutral and Earth on the backup side, an earth fault on any circuit will NOT generate fault current, meaning your RCDs will not trip and metal chassis will remain live to touch. You MUST install an external, fail-safe contactor (normally closed on grid loss) that bridges Inverter Neutral to your local Earth bar strictly when grid power is absent, and opens cleanly before grid re-connecti
I have a Solis Hybrid inverter for my battery system and I was not confident in the limited information I could get out of my installer about earthing when using the EPS socket, so I wonder if your comment would also apply to my system although my system only powers the EPS socket during grid failure which is different to the OP scenario.
I purchased a Condudisc and my installer connected it to the MET rather than the EPS socket, which if I am reading this discussion correctly is actually OK, as they suggest it also would be with a TNS earthing arrangement (mine is TNCS with the Condudisc providing a supplementary earth).
A couple of crucial safety and regulatory points here from someone who installs backup failover and solar storage systems. If you're designing this before bringing in a registered electrician, there are two major things in your current thinking that need immediate correction:
Thank you very much for this input, its exactly what I was looking for, lots to work through and re think over the next few days. I will update my thinking here to see if I've got it or not, if you wouldn't mind giving it a once over then for me. As I say I have limited space for the ATS hence my original consideration of the W2R.
For my clarity my inverter is a SolaX, and SolaX show the strapping the N of the EPS output to the island earth on their own ATS, therefore it is permanent but only comes into play when the grid fails and the SolaX inverter makes the EPS live, does that meet the regs or not please?
Can't use the SolaX ATS as its too big for the space available unless to contents can be put into a smaller enclosure.
Do you know is the SolaX X1-EPS BOX actually meet all the regs etc?
I really appreciate the input I am getting.
I have looked into this and am now confused as my original design thoughts are still the same, can anyone give me clarity please?
Question: When the N-E bond relay operates, as shown in the drawing kindly provided by Msitekkie above, is that not the same as having the N & E permanently bonded that only comes into play when the inverter has switched to Emergency Power Supply mode?
My thinking: I have a SolaX installation, and the EPS port/contacts are not live until a grid failure is detected and the main feed to the house from the inverter has been automatically disconnected. SolaX's own ATS (SolaX X1-EPS Box) I believe does not have a N-E bond relay, as they strap the Neutral of the EPS feed to the island Earth at their ATS. Therefore does that not mean the operating of the internal switching mechanism to turn on the EPS mode is to all intense and purpose acting as the N-E bond relay?
My understanding is this is dependant on the setting in the Inverter, I am thinking of doing the same but sadly do not have room even for the device you show let alone an ATS so was going to go down the EPS essential loads route. In this mode the EPS port is on all the time. It is only in ATS mode that it isn't. The setting is External ATS and it can be enabled or disabled.
The pain of going down the EPS with essential loads route is having to move circuits and also the problem of Inverter failure, though this can be overcome with a changeover switch, well that is the way I was thinking of doing it, effectively bypassing the inverter and feeding the EPS board in the event the inverter fails or need to do maintenance on it.
I would like the whole consumer unit available option that whole back gives you but to be honest the most important thing is lighting and some sockets so The Fridge, Wireless Router and some general power is available.
The main pain is having to move circuits around and you can only have on what you have moved so needs carefull thinking about.
I'm not sure if the SolaX inverter EPS setting is configurable, I was told its main feed or EPS when in grid tied mode, which it needs to be in to shut down correctly when the grid fails.
I considered the essential loads route first of all, but soon dropped that idea as for us, the unpicking and moving of old circuits and/or the provision of new circuits to an EPS config is a massive bit of work...... not worth the upheaval.
It is disabled by default which means the EPS port is always powered you have to enable it for ATS mode. Well that is what Solax manual says I don't own one yet but the essential load board has to have the EPS port powered continuously otherwise the essential loads are dead whilst the grid is up. You only enable it if you have an ATS though obviously or I guess if you have a single socket that you would only use in an emergency.
Yes the downside to the EPS essential loads route is moving the circuits, luckily I can do that fairly easily other wise I really would be looking to somehow shoehorn in an ATS!
Finally, I believe I have a suitable solution for automatic switching from grid to standby power during a grid outage. Thanks to all who have provided input to allow me to get to this design. I look forward to any further commentary if you spot an error, please. The next move if all is good is to talk to local electricians for costing etc.
Many thanks in advance for any further help.
Please note there is a minor error in the above - please read BD2 as DB2 (Garage Consumer Unit)
Note A:
GEYA W2R is an Automatic Transfer Switch, who’s UDEM credentials are # M.2024.206.C108842 valid till 29-10-2029; covering Low Voltage Directive 2014/35/EU /Annex III and EN IEC 60947-6-1:2023.
This particular ATS was chosen due to space limitations, and its back up power supply input being able to support many options including but not limited to generators and inverters. Discussions had with GEYA confirm that it will work perfectly in normal mode even when the power is flowing in export direction from the solar installation as it successfully handles both under and over voltage conditions.
Note B:
The SolaX inverter will be configured to only switch the ā€œEPS port on (live)ā€ when it detects a Grid Anomaly such as frequency or voltage failure, EPS to live will happen immediately following the disconnection of the primary supply to the house which is via DB2.
Because the EPS port is not normally live in this configuration, then the N-E Bonding at the ATS will not be effective until EPS port comes live therefore the action of EPS switching to live also mimics the N-E Bonding relay, I believe fully meeting the regulations.
Note C:
When in EPS mode (island working) BS 7671 Regulation 551.4.3.2.1 requires a suitable independent means of earthing when an EPS supply operates as a switched alternative to a TN public supply; protection by automatic disconnection must not rely on the DNO’s earth, for example the DNO earth may have become disconnected depending on what scenario has resulted in the power outage.