I am sick of being called to "faults" after so called sparkies have been in. The latest on is ridiculous
We recently had a cooker socket installed and it keeps buzzing. Gets there to find that the "new cooker socket" was actually a full cooker circuit. Installed using non-harmonised colours in August 2010.
No RCD Protection on circuit - wired into a Wylex rewirable
Neutral not screwed in terminal correctly - cooker outlet box all cracked and taped over with insulation tape.
Opened cooker socket to find completly burnt out live cable coming from fuse box - customer totally unhappy that I disconnected at fusebox and terminated cable 1 metre away from fuse box so couldn't be reconnected.
Apparently the guy charged £200 to install - NO EIC no PART P Notification, and he no longer operates so nothing can be done
How can these people get away with this