A while back I carried out a PIR on a small industrial unit which is part of a block of 6 or so built around 10yrs ago.First thing I noticed was around the entire perimeter of the block,clipped at ground level to the wall,was a 70mm G/Y single. At each unit a section of insulation had been stripped off and a standard bonding clamp fitted,from this a 16mm went into the unit...this was the earthing system!
Next thing I noticed was that the bonding clamp serving the unit I was testing had come adrift and was flapping in the wind....obviously resulting in no earth at all to that unit. The earth was reconnected and enquiries made as to why this bodge was in place...it appeared that when the place was first occupied there were all kinds of issues with computers going ---- up and the problem was traced to the TNCS earthing system which had been incorrectly installed by the DNO. Dont know what the problem was but the 70mm earth bodge was a temporary fix and has been in place ever since!
Now, Inview of the fact that this 70mm earth,about 300m of it...could go AWOL with the next passing pikey,leaving all the units with no earth...and the poor means of terminating the 16mm to the 70mm which had already come adrift...I coded it 1,although I would accept that a 2 might possibly have been appropriate.
Obviously the PIR was an 'unsatisfactory'...and the owner contacted the DNO......who immediately sent us a very snotty letter saying that it was not our place to condemn their earthing system and as long as the readings were ok they would not do anything about it.....I forgot all about it untill this week when I was at the same place doing a job and the same abortion is in place,only now all the bonding clamps are all corroded and loose on the 70mm.
Sorry for the long winded explanation....but wondered what you guys would do when faced with this on a PIR??....I was pretty much shot down in flames and not backed up by the company....
 
report what you see mate thats all you can do i suppose. your deemed competent to condem an installation for cited reasons and if they what to argue they are arguing with the regs that govern all of us
 
Convert each unit to a TT system if DNO wont install an earth, all they'll say is that they are not obliged to provide a means of earthing.
 
Last edited by a moderator:
Take photos and plenty of them. Fail it again for exactly the same reasons as last time. If the DNO give you uphill that's their prerogative but it makes it their responsibility if there's consequences, fatal or otherwise, in the future.
Just cause someone doesn't like the facts doesn't make it any less of a fact. As Sparky 1502 said you're the competent person so you have a responsibility to report what you see.
Asa footnote, I'm a bit disappointed about the quality of pikey roaming your area :)
 
when all said and done mate, you are there to test and inspect, end of. Yes you have a duty to bring to the attention of the relevant person any dangerous or potentially dangerous situations, but you are under no obligation to fix anything. I try to think like my mate who MOT's the Van. His job is to use his expertise to assess whether or not my Van is safe to be on the road. He will advise me of any problems and likely outcome of not having it fixed. What he can't do is take the van off the road or stop me using it wether it is mot'd or not, and no matter how dangerous it may be.

We have to apply the same thinking when testing and inspecting, we may not like it, but that is how it is unfortunately.

Cheers.........Howard
 
Provided there are a series of electrodes I can almost see the merits of this, although 70mm seems excessive for a TT and it's unacceptable that the clamps should be able to just "come adrift" or corrode away.
At best it's unconventional.
Did you try a Zs from any of the units and/or have I missed the point?
 
Provided there are a series of electrodes I can almost see the merits of this, although 70mm seems excessive for a TT and it's unacceptable that the clamps should be able to just "come adrift" or corrode away.
At best it's unconventional.
Did you try a Zs from any of the units and/or have I missed the point?


I dont mean use the 70mm, cut that off, whack a rod in and rcd the lot.
 
Thanks for the replies guys,
Novus....there are no electodes...it's a cobbled together TNCS, Ze is well within the limits....I'm not really bothered,as far as I'm concerned I failed it on the PIR on grounds of mechanical protection and external influences...and noted the same on the EIC on the recent job....Was more interested really in whether you guys would have coded it and if so what code?...probably should make it clear that the earthing bodge was installed by the DNO.

(secretly hoping that the inefficient pikeys in my neck of the woods do their worst and the units are all live on monday morning!.....Then I'll be able to wave that PIR in their faces and say..."I told you so....what did I say?...but you knew best!!")
 
Last edited by a moderator:
On a different note doing a CU change on a domestic today and noted the guy has a load of new downlights in the kitchen,"He gave me a cert for them" the owner told me.......interesting as there was no bonding in the place and earthing was by means of an VOELCB...He's going to dig out the cert tomorrow,looking forward to seeing it!
 
On a different note doing a CU change on a domestic today and noted the guy has a load of new downlights in the kitchen,"He gave me a cert for them" the owner told me.......interesting as there was no bonding in the place and earthing was by means of an VOELCB...He's going to dig out the cert tomorrow,looking forward to seeing it!

Should be interesting!! let us know how you get on.

Didn't realise the DNO instaled the 70mm earthing bodge. Thats just really bad!!!
 
I dont mean use the 70mm, cut that off, whack a rod in and rcd the lot.
Sorry I meant were there rods in already - I was a bit slow off the mark so didn't see your post before I posted mine.

Could the 70mm be for something else eg lightning protection?
 