A while back I carried out a PIR on a small industrial unit which is part of a block of 6 or so built around 10yrs ago.First thing I noticed was around the entire perimeter of the block,clipped at ground level to the wall,was a 70mm G/Y single. At each unit a section of insulation had been stripped off and a standard bonding clamp fitted,from this a 16mm went into the unit...this was the earthing system!
Next thing I noticed was that the bonding clamp serving the unit I was testing had come adrift and was flapping in the wind....obviously resulting in no earth at all to that unit. The earth was reconnected and enquiries made as to why this bodge was in place...it appeared that when the place was first occupied there were all kinds of issues with computers going ---- up and the problem was traced to the TNCS earthing system which had been incorrectly installed by the DNO. Dont know what the problem was but the 70mm earth bodge was a temporary fix and has been in place ever since!
Now, Inview of the fact that this 70mm earth,about 300m of it...could go AWOL with the next passing pikey,leaving all the units with no earth...and the poor means of terminating the 16mm to the 70mm which had already come adrift...I coded it 1,although I would accept that a 2 might possibly have been appropriate.
Obviously the PIR was an 'unsatisfactory'...and the owner contacted the DNO......who immediately sent us a very snotty letter saying that it was not our place to condemn their earthing system and as long as the readings were ok they would not do anything about it.....I forgot all about it untill this week when I was at the same place doing a job and the same abortion is in place,only now all the bonding clamps are all corroded and loose on the 70mm.
Sorry for the long winded explanation....but wondered what you guys would do when faced with this on a PIR??....I was pretty much shot down in flames and not backed up by the company....
Next thing I noticed was that the bonding clamp serving the unit I was testing had come adrift and was flapping in the wind....obviously resulting in no earth at all to that unit. The earth was reconnected and enquiries made as to why this bodge was in place...it appeared that when the place was first occupied there were all kinds of issues with computers going ---- up and the problem was traced to the TNCS earthing system which had been incorrectly installed by the DNO. Dont know what the problem was but the 70mm earth bodge was a temporary fix and has been in place ever since!
Now, Inview of the fact that this 70mm earth,about 300m of it...could go AWOL with the next passing pikey,leaving all the units with no earth...and the poor means of terminating the 16mm to the 70mm which had already come adrift...I coded it 1,although I would accept that a 2 might possibly have been appropriate.
Obviously the PIR was an 'unsatisfactory'...and the owner contacted the DNO......who immediately sent us a very snotty letter saying that it was not our place to condemn their earthing system and as long as the readings were ok they would not do anything about it.....I forgot all about it untill this week when I was at the same place doing a job and the same abortion is in place,only now all the bonding clamps are all corroded and loose on the 70mm.
Sorry for the long winded explanation....but wondered what you guys would do when faced with this on a PIR??....I was pretty much shot down in flames and not backed up by the company....