Been to a domestic installation today and found that the water and gas are not bonded. The water appears straightforward, however the gas is not so.

The gas service currently enters the house under the floor. A heating engineer has previously teed off here and taken a supply back outside the house and up into the loft to a new boiler installation.

Where would you guys bond to? I'm not keen to bond under the floor - access issues for inspection etc, although this then means that I'm bonding after branched pipework. I could bond outside, near the ground, and run the bonding up the outside wall and across the loft towards the MET on the other side of the house. This may lead to mechanical damage or corrosion issues. Or I could simply bond in the loft where the gas pipe enters.

Any thoughts?
 
The meter cabinet is about 50 metres away at the front of the property (old farm). The gas supply pipe runs underground to the house and pops up at the base of an outside wall.
 
where did you work? mabey you could bond it where the gas pipe enters in the loft.
 
Hi Chops
If this is the nearest point that enters the house you can get to thats fine as long as its bonded.
 
Hi Chops the gas pipe should be bonded within 600m of it entering the property and before any branching off.
 
Agree with these chaps.

As long as its bonded within 600mm etc it doesn't matter where it is.

The certs now have a 'location if not obvious' box now, so just fill that in with the details.
 
Thanks guys

If I go within 600mm and before branched pipework, then its under the floorboards (and carpet / furniture) and then a note on the paperwork and at the CU detailing the location.

Chops
 
Chops,

If you can avoid putting it under the floor then i think that would be better, regardless of noting it on the cert.

Just MHO.:)
 
Well thats the contradiction. I cant satisfy all aspects of the regs here. I cant bond within 600mm of point of entry and before branched pipework and at an accessible point.

It has to be two out of the three. Which aspect do I not satisfy?

Chops
 
I think that as you are familiar with the installation and if under the floor is the only 'satisfying' option, then bond there, again, noting on the cert and as long as it is accessible for future inspections.
 
Hey.

Might be worth a call to your scheme provider as I know the NIC wouldn't accept a main bonding connection under the floor - maintenance and testing reasons.

Cheers
 