Been to a domestic installation today and found that the water and gas are not bonded. The water appears straightforward, however the gas is not so.
The gas service currently enters the house under the floor. A heating engineer has previously teed off here and taken a supply back outside the house and up into the loft to a new boiler installation.
Where would you guys bond to? I'm not keen to bond under the floor - access issues for inspection etc, although this then means that I'm bonding after branched pipework. I could bond outside, near the ground, and run the bonding up the outside wall and across the loft towards the MET on the other side of the house. This may lead to mechanical damage or corrosion issues. Or I could simply bond in the loft where the gas pipe enters.
Any thoughts?
The meter cabinet is about 50 metres away at the front of the property (old farm). The gas supply pipe runs underground to the house and pops up at the base of an outside wall.
Agree with these chaps.
As long as its bonded within 600mm etc it doesn't matter where it is.
The certs now have a 'location if not obvious' box now, so just fill that in with the details.
Thanks guys
If I go within 600mm and before branched pipework, then its under the floorboards (and carpet / furniture) and then a note on the paperwork and at the CU detailing the location.
Chops
Chops,
If you can avoid putting it under the floor then i think that would be better, regardless of noting it on the cert.
Just MHO.:)
Well thats the contradiction. I cant satisfy all aspects of the regs here. I cant bond within 600mm of point of entry and before branched pipework and at an accessible point.
It has to be two out of the three. Which aspect do I not satisfy?
Chops
I think that as you are familiar with the installation and if under the floor is the only 'satisfying' option, then bond there, again, noting on the cert and as long as it is accessible for future inspections.
Hey.
Might be worth a call to your scheme provider as I know the NIC wouldn't accept a main bonding connection under the floor - maintenance and testing reasons.
Cheers
Chops
but the regs aren't statutory they are guidelines so if you can justify your choice and you have done what is reasonably practicable i don't really see a problem ( tin hat on) . So to my mind it's up to you and your decision is right.
location if not obvious?? does that mean anywhere on the pipework as long as it's labelled on the db? where is that in the regs just out of interest? :D
Any thoughts?
hi there
i would suggest you find the gas meter and bond within 600mm before the first branch.
in the cabinet if poss then run to main met
you should not bond under the floor as it is a requirement under the gas regs for access and verification i think this is correct
anybody feel free to please correct me if i am wrong
if you cannot then it is at the first entry point to the building based this assumption from the advice given in the domestic corgi book
hi there
chops has already said gas meter is 50metres in front of property and first bend is under flloor.
Thanks for everones input. I'll forget about under the floor. I will bond where the pipework re-emerges outside the property and then loop into another bond clamp in the loft for belt and braces in case of mechanical damage issues to the outside clamp in the future.
Chops
Reply to Where to bond? in the Australia area at ElectriciansForums.net
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...