L
lurch
Hi
I have to look at a job to install temporary lighting to a scaffold. Apart from the obvious ie. 110volt, weather proof bulkheads is there anything else I should look out for?
Thanks in advance
Hi
Thanks in advance
In my experiance put them up out of reach to stop vandals and if you have any scaffold crossovers/gantrys you may need general lighting as well
Whilst you'll probably want them to be 110V for other reasons, remember that they don't HAVE to be if they're run from an RCD - 704.410.3.10 (ii). You'll also want to earth the scaffold itself.
Maybe i am not reading it correct but hey its good to discuss, 704.410.3.10 A circuit supplying a SOCKET OUTLET with a rated current upto and includding 32a and any other circuit supplying HANDHELD EQUIPMENT
i would see scaffold lighting as fixed equipment?
just a thought
110v flourys as said already be mindfull of crossings Loading bays ect where additional lighting may be required Vandals are an obvious thing Check with main contractor re scaffold moves might mean more cable but may also save you getting called everytime they move a bit with a cable on due to scaffolders inability to undo or cut tywraps without ripping the cable ends from fittings first
also bear in mind the test and inspection 3monthly as this is classed as temporary installation even if its going to be up for 10 years
just a thought
There's nothing really in section 704 that talks specifically about fixed equipment, so I've always worked on the basis that if it's connected via a plug/socket arrangement (as per the vast majority of onsite kit) then it's best classed as a socket outlet - as it is, isn't it?
But, in fairness Note 1. to the reg does go on to say that reduced low voltage is the preferred option for local lighting up to 2kW.
Totally with you i always back everything up with RCD as due course i was just questioning the regs wording,
Where would you like to start picking the 464 pages apart from? We'll need a VERY large pot of coffee, some provisions and a barrel of beer. And probably a masseuse for after.
Hi
Thanks in advance
On many larger sites, there is a requirement for emergency lighting to scaffolds and walkways, may not be relevant here but worth thinking about.
Just love throwing a cat in there sometimes, bring on the beer, lol
Definately, not sure what the regs are but we fit emergencies to arterial routes of the site
One requirement when I wired lights on scaffolds was that the bulkheads at either end were red while the bulkheads in between were white. All wires cable tied to the under side of the tube. All RCD protected.
If the two halves of the scaffolding are separated by wooden panels, you can use the front scaffold poles as the live, then the back as the neutral/earth.
Saves a lot of wire.
emergencys would be worth a look DONT put the cables through scaff poles iv seen this done numerous times
there is 110v led ropelighting on the market we "trialed " it on a big project as they were looking for the greenest stuff it was ok for scaffold and great for stairs but not much cop in open areas as the LEDs werent bright enough
lurch,
mogga,
