things like length of circuits , testing more than 1 ciruit at a time
Tip: read the question, it mentions a conductor, not a circuit
as the length is less, you will have less leakage so a Higher IR reading
In general, the greater the area of insulation there is, the lower the resistance.
As such all of the answers should be 'increase'.
are you sure spin ?, I did mine in December, and Iam almost sure we were told the Csa had no effect on an IR test.
I will stand to be corrected, and bow to superior knowledge
I think you will have to decide yourselves.
Consider why insulation resistance would decrease, then apply it to the various scenarios in the question.
RCD question
b) 200mA
c) 300ms
only 30mA (or less) RCDs used for additional protection are tested @ 5X I delta n
general purpose RCD to BSEN 61008 max = 300ms
general purpose others max = 200ms
Spark, where did you get this information from regarding testing at 5X ?
And the 300ms for BSEN61008, all others at 200ms ?
Hi Ringer,
This is in the OSG, but excludes S types and the types which are 30mA or less which trip in the 40ms required @ 5 X I delta n for additional protection.
This is also in the OSG, but I got the info. from elsewhere, which escapes me at the minute.
red OSG (cos I haven't got the green one yet) pages 91 and 92 sections 11.2, 11.3, 11.4 and 11.5
Hi ringer,
Forgot to mention, apart from the RCDs required to trip in 40 ms,, you only test @ 1/2 Idn and 1X Idn on both halfcycles (only 4 tests)