I have been ask to look at supply a shed/summer house with a supply for a s/outlet and a light. Due to the small load I was going to spur from a socket, swa to shed then a little 2 way cu. this is because the run from the d/b is complicated and involves a lot of remedial work that the customer does not want. My query is what about earthing for the shed. The house is on a tt system, do I have to provide a earth spike or can I export from the met. I am a little worried about my ze reading not being low enough. Also I am a little bit concerns about no discrimination between the shed and house d/b

Many thanks
 
if you are going to spur from a socket with a 13A FCU, no protection is needed in the shed ( except to fuse down to 5A fot lighting) assuming the circuit you are coming off id RCD protected. you can add another earth rod at the shed, no problem.
 
Last edited:
Thanks for the reply,

It is RCD protected as it has RCD as main switc. With an fcu to feed the shed then I will do away with the 2 way board and just fuse down the lights. Would you recommend an earth rod? I have heard different theory's and the regs do not clear it up for me
 
i would fit an additional rod. it may even reduce the Ze of the whole installation. can't do any harm anyway. your problem is going to be that a fault in the shed would trip out the whole house. the ideal way would be to replace the CU with a hi-integrity board and feed the shed from a non-RCD circuit, then RCD in shed, but, as you say, it's a problem feeding from CU, so the FCU option is the easiest and cheapest. just make sure you use a double pole FCU so that you can easily isolate both L and N to the shed in case of a FAULT.
 
i would fit an additional rod. it may even reduce the Ze of the whole installation. can't do any harm anyway. your problem is going to be that a fault in the shed would trip out the whole house. the ideal way would be to replace the CU with a hi-integrity board and feed the shed from a non-RCD circuit, then RCD in shed, but, as you say, it's a problem feeding from CU, so the FCU option is the easiest and cheapest. just make sure you use a double pole FCU so that you can easily isolate both L and N to the shed in case of a FAULT.
not RCD the feed to the shed?...on a TT Tel?...high integrity board with an s type in there....then 30mA in the shed.....
 
Thanks for the reply,

It is RCD protected as it has RCD as main switc. With an fcu to feed the shed then I will do away with the 2 way board and just fuse down the lights. Would you recommend an earth rod? I have heard different theory's and the regs do not clear it up for me

On a TT system, it is always better to have more rods!! But if your going to install an earth rod use at least 2 X 1.2m 5/8'' rods coupled together to give you a decent depth and there-by rod stability. Linked together either directly or via EMT or the steel wire armour of your supply cable...
 