W
Welshsparky
Hi all
Changed a consumer unit today, Advised customer on PIR first but to no avail, so i changed the old consumer unit for a 17th edition dual rcd one, All circuits fine apart from the lighting circuit which trips instantly, Did the standard tests and found allsorts of problems with the neutrals and earths throughout the circuit , Now the problem i have is the entire installation is Pyro , Theirs no loft or floorboards ( second floor flat) so i have no minimal access to cabling, Advised the customer the lighting circuit needs rewiring, But they dont want to go for it and keep explaining to me " It worked before" ( May i also add the customer is polish!!) Now as a temporary measure until i get back their next week ive put the lighting circuit on the mainswitch side of the consumer unit , to atleast give the tenant lighting, Can anybody advise me on the best way to go about this as this work has to be certificated and i dont want to put my name anywere near this lighting circuit !
Many thanks
you need to complete a EIC for the CU change. document the fact that the lighting circuit needs rewiring and the customer refuses to proceed with this.
Is it acceptable to leave the Circuit on the main switch side of the consumer unit though?
Thank you
But you have connected it to a new CU, hence changing the protective device. So you need to put your name to it in one form or another. I always test circuits BEFORE changing CU.... a single borrowed neutral in the wrong place and you've had it. If the customer doesn't agree to works to make a circuit suitable for connection to the new CU, I walk away.
May I also add that my wife is Polish!! Can you believe it?? Cos it's so relevant to the discussion!!
Have you IR tested the pyro to try and locate the fault, chances are the fault will be at an accessory, unlikely that it is damaged in the non accessible areas. Have you/can you trace the fault. Instead of saying it needs a rewire I would complete the EIC and say the lighting needs further investigation to fix and that the customer refuses, that's if he isnt willing to pay you to do this
Does she speak good English? Because the one i'm dealing with doesnt, So to me its extremely relevant because im struggling to get my point across to her. Apart from that thanks for the help :-)
Thank you
you are saying trhat you are leaving the lighting curcuit non-rcd protected. it's no less safe than before, but cover your arse and make sure it's noted on the EIC as a fault that the customer refuses to pay for rectification.
Maybe the thought of a rewire made her uneasy and think about the mess etc it would cause. I'd talk to her and see if she is willing to pay for you to fix the fault/faults.
Id say that was exactly right. ^^^
As it's pyro, if this fault is anywhere other than at an accessory I'll show my bum in Primark window.
Once installed pyro will just sit there for years quietly chugging away and will outlast by many many years a T+E installation. My money is on something being disturbed at a fitting or switch, find that and it's good for flippin years to come
As said above. If they refuse to pay for upgrade and what you have done is not less safe than before. Note it on the cert and Job done :)
I think the ESC deem this an acceptable method Also.
Hi all
Many thanks
be it pyro or t&e theres a fault,just trace it and fix it,as has been said many times mention the word pyro and people panic,its just a cable,too many people rewire to get rid of a basic fault,if it was t&e would you rewire the circuit or fix the faulty leg
Thank you
No its not I hope you fitted a FCU with a 5 amp fuse please say you did if not then you have a 60-100 amp fuse protecting the circuit
Welshsparky,
oldtimer,