Knobhead

I know some countries use protection to guard against a broken neutral in PME systems.
Anyone know how they work?
 
seen it 3-4 times now, last time it had taken out the flexy hoses under the kitchen sink, when they turned the shower on! scarry stuff. but hey they had a good Ze :)

As snowhead says wonder why they dont fit a 100A 500ma RCD before the NE join.
 
Speak to the DNO ask them if you can fit an Earth Rod as a back up they will probably say no but do it anyway lol
J
 
Speak to the DNO ask them if you can fit an Earth Rod as a back up they will probably say no but do it anyway lol
J


That is the way it is done in some countries an external electrode is connected to the N / E juncture within the service head.
 
That is the way it is done in some countries an external electrode is connected to the N / E juncture within the service head.
Most of the underground PME joints to supply buildings are staked by the dno
 
That is the way it is done in some countries an external electrode is connected to the N / E juncture within the service head.

As the N/E are shared at the head can you see any problem with taking a rod from MET ? I am struggling to find a reason how this wouldn't improve the safety of the installation if you lost the Neutral
J
 
I don't quite get where he's saying it should be positioned in relation to it's effectiveness ? My CU has a 30mA non delayed RCD as a main switch will it trip out if the N drops out ? it's the same as his diagram isn't it ?
J
 
I don't quite get where he's saying it should be positioned in relation to it's effectiveness ? My CU has a 30mA non delayed RCD as a main switch will it trip out if the N drops out ? it's the same as his diagram isn't it ?
J

This is looking at loosing the incoming neutral, before the Neutral / Earth connection, the normal C.U RCD can't detect that.
Current flow thro' the C.U rcd won't be any different.
The Green / Yellow ("Earth") now becomes a return waiting for someone to complete the path.
 