A
Andy B
I carried out a ring test and found it wasn`t a ring is there reason they cant be made into 2 x 20A radials.
Your question seems a bit short to really get a full understanding.
There is no reason why not as long you separate it at the board and make other reasonable check and tests on the circuit.
Me too, lol.
If you can identify the end of each leg, then there is no reason you can't convert to two radials.
These faults often concern me as it is not always possible to identify them as two radials (there may be a breakdown in wiring, or hidden connections / accessories). If I can not identify them as two radials, I often change the mcb for a 20A and leave them as one circuit.
Adam summed it up nicely. There is no way on God's beautiful planet that I would simply convert a broken ring into 2 radials without knowing exactly where the break was, and making it safe.
find and verify the ends of each radial before giving each cable its own mcb.
simples
simples
Although, even if you found both ends, can you be sure they are the ends of the two radials, and not spurs from hidden JB's / accessories?
If there are two 2.5mm2 cables on a 30/32A protective device, I always assume it is/was a ring final circuit and would never split (unless I can physically trace both legs to divide into radial circuits).
Just bung them on a 20A and don't worry about the loose connections flapping around somewhere. If there is no continuity on the RFC then it has a fault that needs identifying and rectifying.
well if you have infinity end to end resistance readings for L , N and E between the 2 legs its certainly not a break thats going to reconnect itself if there is a break so i'd still convert to 2 radials.
you'll just have break the circuit down into individual lengths and continuity test each piece.
takes time but it can be confirmed.
and what if the circuit in question is kitchen power and 20amp isnt enough for the connected loads ?
will a 12amp drop in capacity suit the customers power requirements ?
needs more thought than that.
unless it never was a ring to begin with.
in which case you'll be there a very long time trying to find a fault that doesnt exsist.
There is only so much that testing can prove.
I can identify which points each leg is connected to, but I can't confirm that there are no joints or accessories between them that I am not seeing unless I take up every floorboard (if possible), open every chase, pull down the plasterboard ceiling so that I can physically see the wiring routes.
Under the circumstances, this is not practical so I need to better protect the wiring (which is now 2.5mm2) so IMO, a 20A over current protective device is the best I can do (assuming this will not cause an overload problem) after carrying out all other tests on accessible parts of the circuit.
By doing this, I am slightly improving the safety of the circuit by preventing the 2.5mm2 cables from being overloaded.
This is following a PIR with no further knowledge of the installation.
youre working on the assumption that 2 cables sharing an mcb must be a ring with absolutely no evidence to confirm this.
You're assuming I have no evidence.
All other circuits (2 x 2.5mm2's on 30 A MCB's) are Ring Final Circuits, so there is no reason why this one wasn't once a ring final circuit.
All accessories I have located have 2 or 3 cables, and I know where the spurred legs go.
I assume the original electrician installed as per the regs, and the circuit was a ring final circuit. Unless I can safely prove otherwise, the circuit(s) will remain together.
if you split the legs at the CU and measure R1+R2 at each socket ( or use a wander lead and measure R2 ) you will get a pretty good idea of where the discontinuity is. then thinkk about lifting floorboards in that area.
Andy B,
Dannyboy1412,