S
shaun gold
I recently came across an armoured cable on an ECR that was installed in earthed metal trunking from one dis board to another.
Both ends of the armoured had not been glanded off and the SWA had been taped over. As it is enclosed in the tunking and both ends are in the
distribution boards would this be satisfactory as there is an extra core being used as the CPC so the SWA is not needed.
Both ends of the armoured had not been glanded off and the SWA had been taped over. As it is enclosed in the tunking and both ends are in the
distribution boards would this be satisfactory as there is an extra core being used as the CPC so the SWA is not needed.
.... and my input ..... not good practice and very lazy to the extreme it wouldn't have taken long to run a stanley down and rid it of armour, but it should be noted but i wouldn't make too big a fuss as its not really at risk from damage where the armour would be required to be earthed....i think this one off situe would merit a Jobsworth award but its functional as long as the trunking is complete, bet it fails in its use elsewhere like trunking grouping or spacing factors