Went back today, fully armed with 2 meters. Redone all the tests, and the extras. Ze,L-N,L-E,N-E all ok. Done a zs at the loft sockets, all ok.

Not sure why i had problems yesterday, but all good today.!!!!!

Not really found a problem, so im baffled.

I did reterminate the main earth when i removed it to do ze, and i checked all the terminals, including the meter terminals (as the there wasn't a seal on it). Most of the terminals were tight, but a few did turn a bit more, but not to a point that i would say they were loose.

Oh well, i'll be back there next week to finish off, so i will double check the readings again, to make sure.

I would have preffered to have found a definate problem - just to get confidence that everything is ok.

Thanks for all advice.
 
Re: Ze & Zs problems

Sounds like it's down to N-PE potential. Probably caused, as HandySpark suggests, by loading outside that property but before the star point. Maybe yesterday a neighbour was sucking a chunk on another phase (or your phase) causing sufficient load imbalance that was pushing the N away from the bull's eye, and hence moving the N-PE over your meter's error threshold. And today they weren't.

Not familiar with the Fluke, but does it not have a simple 2-wire loop test mode? If so I would test that if you get this "error 4" nonsense next time you test. Also check the Phase-N loop as well, just to get a fuller picture.
 
Last edited by a moderator:
Re: Ze & Zs problems

Sounds like it's down to N-PE potential. Probably caused, as HandySpark suggests, by loading outside that property but before the star point. Maybe yesterday a neighbour was sucking a chunk on another phase (or your phase) causing sufficient load imbalance that was pushing the N away from the bull's eye, and hence moving the N-PE over your meter's error threshold. And today they weren't.

Not familiar with the Fluke, but does it not have a simple 2-wire loop test mode? If so I would test that if you get this "error 4" nonsense next time you test. Also check the Phase-N loop as well, just to get a fuller picture.

The fluke has loads of options for testing. The rotary dial selects the main function and function buttons select options available for that function. I only tend to use the basic options - but since i've had the problem yesterday i've used some of the other functions. The meters relatively new to me, so do not know it inside out.
I have had it calibrated recently, and only noticed last night (whilst reading manual and testing) that it has a parameter for touch voltage that can be set at 25v or 50v. This defaults to 25v when batteries are taken out (which is what the meter was set on during yesterdays tests). However i changed it to 50v for todays tests, but changed it back to see whether error occured, but it didn't - so not sure if that was the problem.

Anyhow, i'm more familiar with the meter now, as a result of yesterdays crusade. And will be a bit more wiser if a similar problem arises in the future. I think i may invest in another meter, possibly just a loop tester as a backup. Being onsite and wondering whether your meter is knackered or youve missed something, is a bit unnerving when the customer is looking over your shoulder all the time, not to mention looking unprofessional if you can't find a definate problem.
:sick:
 
I think i may invest in another meter, possibly just a loop tester as a backup.

Excellent decision,those MFTs are a convenience which are step too far as far as I am concerned
I own one,but woldn't dream of actually using it when I also own individual instruments

They are like a democracy or should I rephrase and say they are like a dictator,they will perform and give results they decide on
Those results also fill me with complete and utter lack of confidence in their purpose
They should come with a ready made container like this Google Image Result for http://www.waeplus.co.uk/img.php/8579/thumb


 
I think i may invest in another meter, possibly just a loop tester as a backup.

Excellent decision,those MFTs are a convenience which are step too far as far as I am concerned
I own one,but woldn't dream of actually using it when I also own individual instruments

They are like a democracy or should I rephrase and say they are like a dictator,they will perform and give results they decide on
Those results also fill me with complete and utter lack of confidence in their purpose
They should come with a ready made container like this Google Image Result for http://www.waeplus.co.uk/img.php/8579/thumb


`seperates Des`...lol.......so would that be a Zpp by any chance Des.....or doubleyourvalue....lol....
 