@Admin You’re asking for how to approach it, so here’s the practical outline –
not a design sign‑off (you still need to do calcs and follow your local regs / DNO rules).
1. Up‑front checks
- Check existing supply (phase, main fuse rating, tails size, earthing type, bonding).
- Check spare capacity in CU / space for new ways or need for small EV sub‑board.
- Confirm DNO notification or approval route for 7 kW EVSE in your area.
2. Typical arrangement (single‑phase ~32 A)
- 7 kW charger = ~32 A at 230 V on its own final circuit.
- Dedicated radial in suitably sized cable (e.g. 6 mm² T&E is common in the UK, but do the volt‑drop, thermal and installation‑method calcs).
- RCD/RCBO per manufacturer’s requirements (Type A + 6 mA DC protection either in unit or upstream, depending on spec).
- Adequate IP‑rated enclosure / switch‑disconnector if required by manufacturer or regs.
3. Cable route & protection
- Plan route from CU to external point: clipped direct, in trunking, buried, or in duct.
- If buried outdoors, comply with burial depth, mechanical protection and marker tape requirements.
- Consider EVSE location re: impact risk, water ingress, cable trip hazards, and minimum heights/clearances.
4. Earthing & bonding
- Check main bonding is up to scratch (gas, water, structural steel where applicable).
- Confirm earthing arrangement; in PME/TT situations follow current guidance on EVSE earthing and open‑PEN protection – use the device type/earthing scheme specified by the EVSE manufacturer and your regs.
5. Testing & paperwork
- Full testing of the new circuit (continuity, IR, Zs, RCD, functional test of EVSE including test box if you have one).
- Issue appropriate electrical cert and EVSE commissioning sheet.
- Notify building control / scheme provider / DNO as required.
If you want, say what country/earthing system you’re thinking of and rough run length / install method, and I can walk through a sample cable size and protective device combo in more detail.