I see your thinking but its use is now been put to a reinforced flex and as so the braiding is affording some form of protection otherwise why use it, because its been utilised in this manor you must treat the shielding as if it were an armour and thus earth it
Some may say the shielding isn't armour, even if the cable is being utilised as a power cable and that it is there purely for reinforcement, not mechanical protection?
if its been used a a tough flex then it would need earthing as damage to the cable could leave the shielding live and EXPOSED at point of damage without any protective device operating.
Damage to any cable could leave a bare line conductor exposed too, that is a faliure of basic insulation that is preventable by either ensuring that the cable in question is suitably selected to afford the correct degree of mechanical protection to suit the environment it is being used in, or by installing the cable in a containment system that offers suitable mechanical protection.
I would argue that if you are installing SY in areas where it is prone to severe mechanical damage, you are either not installing the right cable or not mechanically protecting the cable sufficiently.