I see your thinking but its use is now been put to a reinforced flex and as so the braiding is affording some form of protection otherwise why use it, because its been utilised in this manor you must treat the shielding as if it were an armour and thus earth it

Some may say the shielding isn't armour, even if the cable is being utilised as a power cable and that it is there purely for reinforcement, not mechanical protection?

if its been used a a tough flex then it would need earthing as damage to the cable could leave the shielding live and EXPOSED at point of damage without any protective device operating.

Damage to any cable could leave a bare line conductor exposed too, that is a faliure of basic insulation that is preventable by either ensuring that the cable in question is suitably selected to afford the correct degree of mechanical protection to suit the environment it is being used in, or by installing the cable in a containment system that offers suitable mechanical protection.

I would argue that if you are installing SY in areas where it is prone to severe mechanical damage, you are either not installing the right cable or not mechanically protecting the cable sufficiently.
 
I agree with your points and if you read my previous posts including other threads on this subject you will see i do say its a control cable with screen and some manufacturers state its not to be used as power cable, and yes your correct any cable damaged could leave exposed live conductive part but SY would in my mind be a little more dangerous as it can make the full length of the screening live making it a greater hazard IMHO as any previous damage to the outer cover anywhere along the length with leave yet another area of risk, im going by experience of what i find and the alternatives in some cases is flex which has a lower tolerance to damage hence SY has found it way into its unexpected usage.

I could see we could go round in circles all day and yes see your points but when you've had site visits where people have received shocks from the unearthed screen it tends to be the settler for the debate for me and thus i always earth at supply end at the least, i can walk away knowing its safer than if it wasn't.

The big problem here as we both agree is its found its use more so away from which it was designed and thus the REGs hasn't really covered this situe although i suspect it will be in the 18th it dosn't give a definate solution to refer to and so in this case i choose the safer option.
 
You're right, we could go round in circles all day. Just as many points both for and against a requirement to earth SY braids IMHO.

The big problem here as we both agree is its found its use more so away from which it was designed and thus the REGs hasn't really covered this situe although i suspect it will be in the 18th it dosn't give a definate solution to refer to and so in this case i choose the safer option.

100% agree, hence why I have always earthed! It is such a hotly debated topic that I don't wish to leave myself open to critisism from other sparks or future regs. Still a topic worth discussing though, because if I was inspecting an installation and found unearthed braids, I wouldn't neccesarily be condemning it.
 
Strange thing here D. is my long time mate is called Dave Skelton and its strange talking to a similar name who speaks intellectually as he's as thick as piggy Doo
 
Agree with dark wood (again!!) on this one,if used as power earth both ends, in most inverter installation manuals it shows even the low voltage control cables as shielded earth.

It often gets used on large appliances that get moved regularly,whether that's right or wrong I'm not 100% but it's been regularly done in my 19 years experience.

Saw a lot of rusty failed braiding in the mill,it really doesn't like water that stuff,must nearly all of it WASN'T earthed no doubt it would come live with an impact fault.
 
Saw a lot of rusty failed braiding in the mill,it really doesn't like water that stuff,must nearly all of it WASN'T earthed no doubt it would come live with an impact fault.

As I said before, if you're installing SY in areas where it is prone to impact you're installing the wrong cable. You should be installing either singles in galv conduit, SWA or pyro.
 
Across all these instances, the cable is being used over SWA due to its immensely increased flexibility properties. The screening adds an extra level of mechanical protection and in this case is considered to be an "armour" as such over any other purpose. The environment is not particularly hostile per se, but the fools who work here are the main threat. That being said, i have taken an average height of all employees and then deciphered a height which is not accessible by the common numpty.

However, i shall invest of some of those zinc stuffing glands as shown previously, and earth away... like normal.

Hope you all had a good weekend! Thanks for the replies.