christ i give up!!!couldnt find the watts anywhere not even on screwfix website. the side of the box is 2.7kw for 230v or 3kw for 240v. The boiler is on same circuit so should i fit the 20amp? or should i run the boiler off the 6amp, and imm of a 16amp. will be calling the sparky back as he fitted the 6amp.
couldnt find the watts anywhere not even on screwfix website. the side of the box is 2.7kw for 230v or 3kw for 240v. The boiler is on same circuit so should i fit the 20amp? or should i run the boiler off the 6amp, and imm of a 16amp. will be calling the sparky back as he fitted the 6amp.
couldnt find the watts anywhere not even on screwfix website. the side of the box is 2.7kw for 230v or 3kw for 240v. The boiler is on same circuit so should i fit the 20amp? or should i run the boiler off the 6amp, and imm of a 16amp. will be calling the sparky back as he fitted the 6amp.

OK ..... it's a 16 amp MCB you need for this immersion heater and - as Tel says - 2.5mm T&E cable.
The 2.5 T&E goes from the 16 amp MCB in the consumer unit to a 20 amp switched flex outlet something like this: 20 Amp DP Switch with Flex Outlet and Neon next to the immersion heater & from there a bit of 2.5 3 core heat resisting flex to the immersion heater itself.
I'm not normally this helpful, but it's Christmas.![]()
couldnt find the watts anywhere not even on screwfix website. the side of the box is 2.7kw for 230v or 3kw for 240v. The boiler is on same circuit so should i fit the 20amp? or should i run the boiler off the 6amp, and imm of a 16amp. will be calling the sparky back as he fitted the 6amp.
He either doesnt exist, or doesnt have a clue what he's doing. Daz
My money is on "doesn't exist"
I don't think it's about being perfect. A couple of questions to begin with:
Why are you asking on here what size MCB to buy for your electrician?
Why has your electrician fitted a 6A MCB for an immersion heater?
Why are you buying parts at all when you don't even know what a kW is?
Daz
Oh let me see on this erm I can get electrical parts at cost, or even free for that instance. 2nd I dont know why he fitted a 6amp. and i know exactly what a kW is where have i ever posted that!
couldnt find the watts anywhere not even on screwfix website.