Currently reading:
SWA Armour
Discuss SWA Armour in the UK Electrical Forum area at ElectriciansForums.net
davel81
Hi
Ive got to run in some SWA cables for some large bits of equipment. Its TP&N, is there any issues with using 4 core and using the armour for the earth (ensuring the Zs is ok)?
There's a thread on here about this very subject and someone posted a table showing what was acceptable and what was not, so if you find it you'll know long before you do your Zs test.
as long as the armour is of sufficient csa. generally all SWA up to 90mm complies. some of the xlpe SWA doesn't.
As long as the armour meets the requirements then theres no problem at all...
Earthing Nuts - Speed up metal cable gland installation and EMI / RFI screening
Have a look through table 5 under technical info...
THROW THAT DAMMED TABLE AWAY!! It causes more confusion, than any help!!
Use this table where all the calculations have been done for you...
Blue = min CSA of cables SWA to comply.
(Red) = Cable does not comply.
Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.
Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
15
16
17
2.5
5.7
17
19
20
21
23
35
24
36
40
41
44
49
16
36.1
46
50
72
25
36.1
60
66
76
35
36.1
66
74
84
50
56.4
74
84
122
70
79.0
84
119
138
95
107.2
122
138
160
120
135.3
(131)
150
220
150
169.2
(144)
211
240
185
208.6
(201)
230
265
240
270.6
(225)
(260)
299
300
338.3
(250)
(289)
(333)
400
403.9
(279)
(319)
467
Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.
Conductor CSA
1.5
3.4
16
17
18
2.5
5.7
17
19
20
19
21
23
22
23
36
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138)
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
452
Remember these tables refer to complying with CPC requirements, They do NOT refer to Bonding CSA requirements...
Reply to SWA Armour in the UK Electrical Forum area at ElectriciansForums.net