After a bit of advice/clarification re 18[SUP]th[/SUP] edition of the regulation.
Firstly a bit of background, having a lot of work done on a 70's bungalow for my mother in law, altering the layout, lounge/dinner to a kitchen/dinner with separate lounge, new bath room, new external oil boiler and included a complete rewire.
There have been a few points raised by the electrician of which I found a bit strange.
He wanted to move the meter and I said no as it is fine where it is and I did not want to fall foul of any of the supply company regulations.
I wanted one double pole switch for the oven (Total connected load 3.68KW) and the hob (Total connected load 2.99KW) and he wanted two, both are well within 2 meters of the switch position I had in mind. The reasoning here is glass splash backs and the less holes the better a each hole adds to the cost.

Earth bonding to the water main he wanted the stop cock under the kitchen sink as he said “that’s where they go” and I have opted for a remote (Surestop) one which is plastic and the incoming pipe is plastic, and only picks up copper under the bathroom floor. The reason for picking a remote one is that in the event of a leak an elderly person would have problems with the older brass tap never mind getting to it. Does this earth connection need to be assessable? It is going to be under the floor in an area that is not readily accessible as it will be tiled.
The new main CU is having all RCBOs fitted so I’m thinking that any supplementary bonding is only precautionary rather than a requirement.

Garage supply in armored cable not a problem there and I was going to use a plastic garage CU but he said he would have a problem with the termination but I thought what’s wrong with a metal box along side the CU for the termination of the armored cable.

Any comments welcome good or bad and have I missed anything I need to be aware of.

Rob
 
I really can't help you with the 18th edition as I don't have doc and Marty McFly with me right now it is 17th still.
 
Well quickly...
Incoming plastic services do NOT need bonding
He CANNOT legally move the meter....but this is done a lot
I would go with two isolators but I put them in cupboards, no requirement to put them above the work top
 
After a bit of advice/clarification re 18[SUP]th[/SUP] edition of the regulation.
Think you may mean the 17th

He wanted to move the meter and I said no as it is fine where it is and I did not want to fall foul of any of the supply company regulations.
No he shouldn't be moving that - DNO (supply companies) property

I wanted one double pole switch for the oven (Total connected load 3.68KW) and the hob (Total connected load 2.99KW) and he wanted two
Both can go on one switch thats not a problem

Earth bonding to the water main he wanted the stop cock under the kitchen sink as he said “that’s where they go” and I have opted for a remote (Surestop) one which is plastic and the incoming pipe is plastic, and only picks up copper under the bathroom floor. The reason for picking a remote one is that in the event of a leak an elderly person would have problems with the older brass tap never mind getting to it. Does this earth connection need to be assessable? It is going to be under the floor in an area that is not readily accessible as it will be tiled.
The earth clamp needs to go where it can be easily accessed for inspection, within 600mm of where it enters building or as near as practically possible


The new main CU is having all RCBOs fitted so I’m thinking that any supplementary bonding is only precautionary rather than a requirement.
Not required

Garage supply in armored cable not a problem there and I was going to use a plastic garage CU but he said he would have a problem with the termination but I thought what’s wrong with a metal box along side the CU for the termination of the armored cable.
Nothing wrong with using an adjacent metal box


 
After a bit of advice/clarification re 18[SUP]th[/SUP] edition of the regulation.
Firstly a bit of background, having a lot of work done on a 70's bungalow for my mother in law, altering the layout, lounge/dinner to a kitchen/dinner with separate lounge, new bath room, new external oil boiler and included a complete rewire.
There have been a few points raised by the electrician of which I found a bit strange.
He wanted to move the meter and I said no as it is fine where it is and I did not want to fall foul of any of the supply company regulations.
I wanted one double pole switch for the oven (Total connected load 3.68KW) and the hob (Total connected load 2.99KW) and he wanted two, both are well within 2 meters of the switch position I had in mind. The reasoning here is glass splash backs and the less holes the better a each hole adds to the cost.

Earth bonding to the water main he wanted the stop cock under the kitchen sink as he said “that’s where they go” and I have opted for a remote (Surestop) one which is plastic and the incoming pipe is plastic, and only picks up copper under the bathroom floor. The reason for picking a remote one is that in the event of a leak an elderly person would have problems with the older brass tap never mind getting to it. Does this earth connection need to be assessable? It is going to be under the floor in an area that is not readily accessible as it will be tiled.
The new main CU is having all RCBOs fitted so I’m thinking that any supplementary bonding is only precautionary rather than a requirement.

Garage supply in armored cable not a problem there and I was going to use a plastic garage CU but he said he would have a problem with the termination but I thought what’s wrong with a metal box along side the CU for the termination of the armored cable.

Any comments welcome good or bad and have I missed anything I need to be aware of.

Rob
that plastic garage board....whatch him on that one wont you.....i can smell jointing onto flat twin with a throughbox here for that armoured.....its really bad and i dont like it at all stuff like that......i`v seen it a few times....
 
After a bit of advice/clarification re 18[SUP]th[/SUP] edition of the regulation.
Firstly a bit of background, having a lot of work done on a 70's bungalow for my mother in law, altering the layout, lounge/dinner to a kitchen/dinner with separate lounge, new bath room, new external oil boiler and included a complete rewire.
There have been a few points raised by the electrician of which I found a bit strange.
He wanted to move the meter and I said no as it is fine where it is and I did not want to fall foul of any of the supply company regulations.
I wanted one double pole switch for the oven (Total connected load 3.68KW) and the hob (Total connected load 2.99KW) and he wanted two, both are well within 2 meters of the switch position I had in mind. The reasoning here is glass splash backs and the less holes the better a each hole adds to the cost.

Earth bonding to the water main he wanted the stop cock under the kitchen sink as he said “that’s where they go” and I have opted for a remote (Surestop) one which is plastic and the incoming pipe is plastic, and only picks up copper under the bathroom floor. The reason for picking a remote one is that in the event of a leak an elderly person would have problems with the older brass tap never mind getting to it. Does this earth connection need to be assessable? It is going to be under the floor in an area that is not readily accessible as it will be tiled.
The new main CU is having all RCBOs fitted so I’m thinking that any supplementary bonding is only precautionary rather than a requirement.

Garage supply in armored cable not a problem there and I was going to use a plastic garage CU but he said he would have a problem with the termination but I thought what’s wrong with a metal box along side the CU for the termination of the armored cable.

Any comments welcome good or bad and have I missed anything I need to be aware of.

Rob

Out of interest who is actually doing this design and work? You or your "electrician"??
 
After a bit of advice/clarification re 18[SUP]th[/SUP] edition of the regulation.
Firstly a bit of background, having a lot of work done on a 70's bungalow for my mother in law, altering the layout, lounge/dinner to a kitchen/dinner with separate lounge, new bath room, new external oil boiler and included a complete rewire.

There have been a few points raised by the electrician of which I found a bit strange.

He wanted to move the meter and I said no as it is fine where it is and I did not want to fall foul of any of the supply company regulations.

Not enough information to comment!!

I wanted one double pole switch for the oven (Total connected load 3.68KW) and the hob (Total connected load 2.99KW) and he wanted two, both are well within 2 meters of the switch position I had in mind. The reasoning here is glass splash backs and the less holes the better a each hole adds to the cost.

One cooker control switch is all that is required, connect the two appliances below and behind cabinets via a dual conection plate. Have you made a mistake on the Hob rating, it seems to be very low??

Earth bonding to the water main he wanted the stop cock under the kitchen sink as he said “that’s where they go” and I have opted for a remote (Surestop) one which is plastic and the incoming pipe is plastic, and only picks up copper under the bathroom floor. The reason for picking a remote one is that in the event of a leak an elderly person would have problems with the older brass tap never mind getting to it. Does this earth connection need to be assessable? It is going to be under the floor in an area that is not readily accessible as it will be tiled.

If the pipe entering the building is copper/metal then it WILL need bonding, if plastic, it will obviously not require a bonding connection. All bonding connections to service pipework etc needs to be accessible, and should never be located under the floor!! The boilers pipework may well need bonding, and be confirmed by testing. The incoming Gas pipework WILL need bonding back to the MET

The new main CU is having all RCBOs fitted so I’m thinking that any supplementary bonding is only precautionary rather than a requirement.

There should be no need in your case for supplementary bonding in the bathroom etc

Garage supply in armored cable not a problem there and I was going to use a plastic garage CU but he said he would have a problem with the termination but I thought what’s wrong with a metal box along side the CU for the termination of the armored cable.

Nothing wrong with using a metal adaptable box to terminate a SWA cable before entering a plastic CU. I wouldn't have any trouble myself, terminating directly to the plastic box!! SWA sheath earthing is maintained via an earthing nut or banjo and fly lead.

Any comments welcome good or bad and have I missed anything I need to be aware of.

Rob

Others may have other/further comments...
 
Leave your spark alone, sounds like he knows the regs relatively well and he trying do to a better job than required....Hat off to him. For example:

All RCBO's on CU
Glanding straight into a metalclad CU
Wanting the water stop clock under the kitchen sink (much easy for sparks in future when they come to test - first place we look)

What a top bloke!
 
Leave your spark alone, sounds like he knows the regs relatively well and he trying do to a better job than required....Hat off to him. For example:

All RCBO's on CU
Glanding straight into a metalclad CU
Wanting the water stop clock under the kitchen sink (much easy for sparks in future when they come to test - first place we look)

What a top bloke!


To add to this..... He's the one who's carried out the 4 year apprenticeship also and I'm sure he has the up to date.... 17th!!! edition regs!
 
Choose the the most suitable accessory positions from the choice that the installing electrician gives that comply with the regulations

It's best to leave the compliance with the regulations to the electrician,he should be more than aware of what is required and probably is just that



Unless of course,you have doubts about his suitability,but having engaged him for his skill,why doubt his suitability at this late stage
 
To add to this..... He's the one who's carried out the 4 year apprenticeship also and I'm sure he has the up to date.... 17th!!! edition regs!


In years gone by maybe!! ...Now day's it is just as likely he is a fast track wanna-be electrician!! lol!!

And that's just the trouble, there is no up front distinction between the fully trained and experienced and the under trained inexperienced guy that turns up on your door step!!
 