edexlab

~
Arms
View attachment pg1.pdfView attachment pg2.pdfView attachment pg3.pdfView attachment pg4.pdf

I was going to call this thread spot the mistake but that would take up too much time, should be spot the correct bits

This is a certificate from a domestic job I went to just before the holidays the Electrician involved had done numerous things extremely badly mainly poor workmanship while adding to existing circuits and here's a brief list

10mm main earth on TNC/S with 25mm tails 100A incomer

No cpc on lighting circuit throughout but he'd fitted a metal light fitting in kitchen

No Rcd protection on circuits in the bathroom or kitchen

Used the cpc in a twin and earth to use as a three core strapper for the two way switching in the kitchen

New consumer unit was a mess of sphagetti, holes at the bottom where you could easily touch the busbar(I'll post pictures if possible later)

Connected the bathroom lights into existing double insulated single lighting circuit via separate Jb's which then had twin with cores cut off ie line to one jb neutral to the other this was again a mess of cable just left tangled

The shaver skt is jb'd to the shower circuit 6.0mm although he had put it on a 10A Mcb (I know you could argue this one but I'd seen enough of his work and as these rooms were gutted theres no excuse not to do it properly)

In the Kitchen (small kitchen approx 3 x 3.5m)

3 skts via 2.5mm t&e connected to the old cooker circuit 6.0mm on a 32A Mcb

There were 2 Skts/ 1 Fcu on a radial 2.5mm on 32A Mcb

1 radial circuit comprising of 2 x 2.5mm t&e feeding two skts again on a 32A Mcb
this meant that there were 4 circuits feeding skts within the kitchen, which I think is bad as customer turns the mcb marked up sockets off at the consumer unit thinks they've isolated it and gets a shock as only the one socket in the kitchen is fed from this circuit

Loose connections on everything he'd touched

A complete lack of correct labeling and the certificate is baffling I couldn't believe someone would be so stupid to actually sign it, its no wonder he refused to revisit the job which is about 300 metres from his own door step

He's not registered with a scheme and the LABC were not notified this is someone who works in a family Business mainly commercial works ie schools and supermarkets I hope he's on this forum and is suitably embarrassed!
 
Last edited:
You shouldn't of erased his name. If people can't be arsed to open them up in adobe...which i was tempted... do it, its terrible.
 
love how he's got ring readings for every single circuit.

How has someone like that passed inspection and testing :|
 
No requirement for RCD protection to circuits of a kitchen.
But yes, the 16th edition paperwork is a mess, and if it's anything to go by, so is the work.
I love the fact that it's a combined TN-S and TN-C installation.
 
To be fair - i think thats the worst cert ive actually ever seen.

Supervising an apprentice on filling them out (on old pads), they get the occassional thing wrong, but nowhere near as bad as that. He's definitley not had any training.
 
The Customer had his own Electrician have a check on this newly bought property and he walked off absolutely livid and as he's quite busy the job came to us , I couldn't work out what he was actually signing for on the cert never mind the actual content being 90% incorrect I want to know where he got his Zs reading from for the lights (no cpc) they didn't teach me that at college!
 
Quality certificate. It is an absolute disgrace that some people will do work like that and get away with it time and time again. I would have thought that the "Scams", oops, I mean governing bodies would be all over work like this. Did you report it to a your "scam"? If enough of us keep annoying the scam lords by reporting unsafe work maybe they will get off there backsides and do something for all the money they get every year and drive up the standards. Alas I fear there is little hope though. Minor rant over!
 
[/QUOTE]New consumer unit was a mess of sphagetti, holes at the bottom where you could easily touch the busbar(I'll post pictures if possible later)[/QUOTE]

Aye, if you could - post them in this thread, sound's comical.
 
No requirement for RCD protection to circuits of a kitchen.
But yes, the 16th edition paperwork is a mess, and if it's anything to go by, so is the work.
I love the fact that it's a combined TN-S and TN-C installation.

socket outlets no RCD this job was done last october so 17th ed also he's got readings and ticked for an earth electrode
 
diabolical. can someone tell me when BS7671 was amended in 2012. i must have missed the 2nd amendment.
 
I've saved that cert - can't actually believe how stupid it is.

Also, just noticed Glenn is viewing the thread, with his fine english i wonder what words are gonna come flying out :laugh:
 
No requirement for RCD protection to circuits of a kitchen.
But yes, the 16th edition paperwork is a mess, and if it's anything to go by, so is the work.
I love the fact that it's a combined TN-S and TN-C installation.

Did you miss the Earth Rod reading then?? lol!! Dam good-un too at 0.80 ohms!!
 