What will happen or the consequence of using the neutral of Y transformer IT system. I've read that neutral should not be used for IT system but dont know the reason behind. Cheers.
 
Because of the danger of voltage rise in the neutral if there were to be an L > E fault. This would be up to 6350V on an 11 KV system.

What voltage are we talking about?
 
Thanks Tony! Do you mean the voltage of neutral with respect to earth? So it has something to do with cable insulation? Other than that the system will be fine? Actually, i just read it in the net.. this is how it goes :
The ungrounded power system shown in Figure 3 is typically found in older industrial power systems. This system allows continuity of power after the occurrence of the first line-to-ground fault. The first line-to-ground fault simply causes the system to become grounded. Since there is no path for ground fault current to flow, overcurrent protective devices will remain closed. A means to detect the occurrence of a ground fault is required. In an ungrounded system, line-to-ground voltages could exceed line-to-line voltage due to transients and other abnormal conditions. Since the neutral is not solidly grounded, line-to-neutral loads cannot be served with this system.
[FONT=UniversCondensed,Bold][FONT=UniversCondensed,Bold]
[/FONT]
[/FONT]
[FONT=UniversCondensed,Bold][FONT=UniversCondensed,Bold][/FONT][/FONT]
 
No i'm not.. i just read it in rockwell automation website i think and puzzled by the last sentence. Just wanna know the reason why...

Anyway, many thanks for your time Tony!
 
IT (double fault) systems are supplied via an isolation transformer, and will be monitored/protected by insulation devices. It is the system of choice in hospital operating theatres, in both Europe the USA as well as many other countries.

Also used with magnetic lift cranes, where a loss of power to the magnetic lifting device can be catastrophic
 
I've worked on a ship and we also use IT system and continues supply of power is a priority as what you've said engineer54.. but what does this sentence mean : ''Since the neutral is not solidly grounded, line-to-neutral loads cannot be served with this system''.


Cheers!
 
I've worked on a ship and we also use IT system and continues supply of power is a priority as what you've said engineer54.. but what does this sentence mean : ''Since the neutral is not solidly grounded, line-to-neutral loads cannot be served with this system''.


Cheers!


No idea!! Perhaps they are talking about a supply type transformer, but never seen one. lol!!
As i said IT is normally derived from an isolation transformer, eg 400V in 400V out, ...leaving the earthing system for the incoming supply behind.... No idea how an IT system is distributed on a ship...
 
On the ship, neutral of geny is floating, distribution tx is delta-delta. 1 phase loads are somehow divided equally on each phase by the shipyard during ship building i guessed...
Maybe i have to let go of that 'sentence'... LOL. can't find the answer on the net...
 
haven't got a clue either,I wouldn't try asking cheif electrician as they are usualy hiding or p*&sed. one of our workers asked him to make them a cable up instead of me and he wirred earth to line.
 
On the ship, neutral of geny is floating, distribution tx is delta-delta. 1 phase loads are somehow divided equally on each phase by the shipyard during ship building i guessed...
Maybe i have to let go of that 'sentence'... LOL. can't find the answer on the net...

It can be done, but needs a high impedance ZigZag secondary reference transformer.
 
What most forget, is that being a double fault earthing arrangement, it's a pig of a job finding the fault, on the occasion of a 1st fault which the insulation monitoring device will have sensed and be indicating by an alarm buzzer/bell...
 
What most forget, is that being a double fault earthing arrangement, it's a pig of a job finding the fault, on the occasion of a 1st fault which the insulation monitoring device will have sensed and be indicating by an alarm buzzer/bell...

Tell me about it. Three months to find an intermitent fault on a furnace. Molten iron occasionally dripping on to the induction coil. When I found it I wished I hadn’t, I was stood under the leak.
 